TSSM - Two-sensor Symmetrical Muting
Krone
Oct 2020
Denmark
Hi Guys
I hope you can help me with the TSSM block in studio 5000
I am using it for a LC to control the muting.
The muting of the LC works fine when it sees the object coming into the muting sensors, regardless of S1 or S2 falls first. Then the object goes through the LC and after that the problem occur. If S2 gets signal first (a few ms) before S1 the block fails, but if S1 gets signal first, then everything works fine.
Since this is a symmetrical I would assume that is does not matter if S1 or S2 would be the last to activate again after the LC, as long as it is done before the discrepancy time, or am I completely wrong?
According to the documentation, you can set the S1-S2 Discrepancy
Time which is the maximum amount of time the muting sensors
(Sensor 1 and Sensor 2) may be inconsistent before
a fault occurs
Here is a link to my current setup:
https://imagesharing.com//photo.php?s=yv6h8udp
NOTE: The MuteLC_In.O1 are not used
Br
Anders
Instruction help states:
Sensor 1 must be blocked or cleared within the S1S2 Discrepancy Time of Sensor 2 being blocked or cleared.
Sensor 2 must be blocked or cleared within the S1S2 Discrepancy Time of Sensor 1 being blocked or cleared.
I take this the same way as you. The order should not matter. Watch for some kind of flicker on the inputs,
maybe use a longer filter in the module configuration? Just a suggestion.
Side-to-side location of the package could throw the timing off...
I tried with a flicker and that gave the same result.
But i figured it out. The S1,S2-LC minimum time also have to expire after the LC has been re-established, before the muting sensors may see eachother again, otherwise it will fault.
Hi everyone, I am working with micro850, a proximity sensor (FOTEK, PL-05P) and a 3DOF serial arm robot. I use MC_MoveRelative to control the...
57
Maybe a stretch to call this a PLC question, but it does connect to a PLC input. I have two German switches: Sick WL9LG-3P2232 And a...
109
Hi, Need help with coding for a faulty component sensor which we are using a push button as we are using a test rig. the plc is a allen bradley...
207
Hi all, I am implementing an incremental encoder sensor (ABZ) to replace the existing "manual" encoder wheel I have in my device. This is a 360...
166
I am looking for temperature/humidity sensor recommendations. Would like the sensor to display temp and humidity. Need to connect to a Contrologix...
226