Thanks George your througher response is greatly appreciated.
To clarify Active overload is all we require, so once configured to trip at a certain trip point I/the end user is happy as we see the status of the outputs physically via IO through the downstream contactor. NO logic, no control of the additional IO..

I did think CIP messaging would be okay just to see earth leakage trip and or average current.



The customer is pretty hard and fast set on L16 for their compactlogix controllers, dont ask, but ive seen two side by side..

When I compiled the project, maybe 50 times not once did throw a warning or error with the ethernet Tree configured for 11 nodes. ( Logix 5000 30.11 version).


I appreciate all your guys responses, I think this will help others in the future!
  Reply With Quote
Old January 21st, 2020, 02:45 PM   #17
Ken Roach
Lifetime Supporting Member + Moderator
United States

Ken Roach is offline
 
Ken Roach's Avatar
 
Join Date: Apr 2002
Location: Seattle, WA
Posts: 15,676
If you agree to this customer's demand to build the machine using the 1769-L16, you will come to regret doing so.

You will get their accolades for saving money on the hardware. You may get the satisfaction of "doing what people said couldn't be done".

But shortly after that first machine is delivered to the remote outback, you will come to regret it.

By then the cabinet will be too small, the Ethernet switch too paltry, the budget long since spent. You will absorb the blame for the excess costs, the lost production, and the consequential results of the machine system's failure.

You are doing a disservice to your customer, your employer, and your own professional reputation.

I've made this mistake, and fixed this mistake for others, enough times to recognize it when I see it in process.
  Reply With Quote
Old January 21st, 2020, 03:03 PM   #18
Phrog30
Member
United States

Phrog30 is offline
 
Join Date: Dec 2006
Location: Montgomery, Alabama
Posts: 714
Quote:
Originally Posted by Ken Roach View Post
If you agree to this customer's demand to build the machine using the 1769-L16, you will come to regret doing so.

You will get their accolades for saving money on the hardware. You may get the satisfaction of "doing what people said couldn't be done".

But shortly after that first machine is delivered to the remote outback, you will come to regret it.

By then the cabinet will be too small, the Ethernet switch too paltry, the budget long since spent. You will absorb the blame for the excess costs, the lost production, and the consequential results of the machine system's failure.

You are doing a disservice to your customer, your employer, and your own professional reputation.

I've made this mistake, and fixed this mistake for others, enough times to recognize it when I see it in process.
Very well said. Couldn’t agree more.
  Reply With Quote
Old January 21st, 2020, 04:54 PM   #19
ASF
Lifetime Supporting Member
Australia

ASF is offline
 
Join Date: Jun 2012
Location: Australia
Posts: 3,156
Screenshot of a v30.11 project with an L16ER-BB1B that I just set up for testing.

I agree with Ken and the others - you are setting yourself up for a huge fall if you persist with this option. Part of your job as an engineer is to understand the requirements and limitations of a system better than the customer, and to be able to convey the requirements to the customer in a way that they understand. The customer is not always right.

I would honestly recommend walking away from the job if the customer won't budge from a flawed design. Let someone else own the headache.
Attached Images
File Type: png Screen Shot 2020-01-22 at 8.50.31 am.png (41.0 KB, 62 views)
  Reply With Quote
Old January 22nd, 2020, 01:26 AM   #20
janner_10
Lifetime Supporting Member
United Kingdom

janner_10 is offline
 
Join Date: Dec 2014
Location: Tewkesbury
Posts: 1,101
We have a couple of these customers that think they know best. The pay more once we add on the c**t Tax.
  Reply With Quote
Old January 22nd, 2020, 03:30 PM   #21
Geospark
Lifetime Supporting Member
Ireland

Geospark is offline
 
Geospark's Avatar
 
Join Date: Feb 2012
Location: Kildare
Posts: 2,934
Quote:
Originally Posted by Sydneyguy
...The customer is pretty hard and fast set on L16 for their compactlogix controllers, dont ask, but ive seen two side by side...
I don't need to ask!

Are they paying you to talk or listen?
__________________
"A little nonsense now and then is relished by the wisest men".
  Reply With Quote
Old January 26th, 2020, 07:30 AM   #22
Sydneyguy
Member
Australia

Sydneyguy is offline
 
Join Date: Jun 2019
Location: Sydney
Posts: 27
Quote:
Originally Posted by Geospark View Post
I don't need to ask!

Are they paying you to talk or listen?

Listen, Think, Solve
  Reply With Quote
Old January 26th, 2020, 05:41 PM   #23
Geospark
Lifetime Supporting Member
Ireland

Geospark is offline
 
Geospark's Avatar
 
Join Date: Feb 2012
Location: Kildare
Posts: 2,934
Quote:
Originally Posted by Sydneyguy
Listen, Think, Solve
Or in their case...

Lessen, Tinker, Save
__________________
"A little nonsense now and then is relished by the wisest men".
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
SLC Master Controller PID plcnovel LIVE PLC Questions And Answers 8 July 20th, 2009 01:14 PM
PIC Controller on GE 90-30 denman_100 LIVE PLC Questions And Answers 2 July 7th, 2008 10:37 AM
CONTROLNET - Not recognizing new Nodes? shiftedbits LIVE PLC Questions And Answers 28 June 2nd, 2007 05:34 PM
What is this ? KTM Rider LIVE PLC Questions And Answers 28 September 10th, 2006 07:56 PM
Automatic and Manual controller mode and it's PID form Pandiani LIVE PLC Questions And Answers 11 September 10th, 2006 07:29 PM


All times are GMT -5. The time now is 02:36 AM.


.