Red Lion Hmi failures

ADMW

Member
Join Date
Sep 2020
Location
BC
Posts
1
I have some red lion g306A Hmis connected to a Dh485 network with 4 slc 5/03 and 1747-aic modules and I keep burning out comm ports on the screens. there are slc 500s connected 2 at a local station and the other 2 are at a remote station with areial comm line in between. the engineer that installed the screens originally recommended some phoenix contact rs485 isolation repeaters to isolate the comm line. So I installed the siemens equivalent (my wholesaler is a siemens dealer) rs 485 repeater they seemed the same except the siemens didn't have a spot for the common wire. so I ran the wire through a 24V surge protector and installed the new HMI which lasted only a day or so before the comm port was toast again. Does any one have any ideas on testing to see what is going on or ideas for products that could help me get these hmis to last.


Thanks
 
they seemed the same except the Siemens didn't have a spot for the common wire.

Are you sure they're ordinary RS485 isolators, or are they for Profibus DP ?

DH485 is a true isolated differential RS485 circuit, so it really does use an isolated signal common wire, as well as two differential signal wires. It does not use ground or chassis ground as the reference to the RS485 signal like Profibus DP does or like some RS485 devices can.

Get a meter on those RS485 terminals and see what kind of voltages you're seeing between the common and the signal, and between those and actual earth ground.
 

Similar Topics

I am having issues getting a Red Lion HMI and Micro830 controller to communicate. I am using the cable here to connect the controller to the RS232...
Replies
0
Views
117
Hi I need to send a null command down a comms port. But in the crimson software when i used /x00 it coming back "Cannot use null character is...
Replies
2
Views
420
Hi Everyone, I am hoping a Red Lion Expert can point me in the right direction. I am experimenting with data logging on a CR3000 10" screen...
Replies
4
Views
603
I have a Red Lion G09 scanning 8 Invertek P2 VFDs via modbus RTU - I've setup necessary comms and tags and all works well. I have a 'Settings'...
Replies
3
Views
1,873
Has anyone ever replaced a touch screen on a legacy Red Lion G3 series HMI?
Replies
12
Views
1,454
Back
Top Bottom