ABB ACS550 Earth Fault
I just replaced this drive as the old one went out when the plant had a power surge/flicker.
1-Installed the drive 2-Powered up 3- Got an immediate EARTH FAULT, so I check the manual and it talks about wires being grounded. 4- Disconnected wires from the motor and ohm out the wires to ground( CHECKS GOOD) 5-So I ohmed out the motor and I was getting 40-50 ohms when tested to ground. ![]() 6-I have not powered up the drive with out the wires disconnected. I will try that next to confirm my thoughts that the motor windings are starting to go bad and current is leaking out. Bad motor? |
![]() |
![]() |
#2 |
Lifetime Supporting Member
|
Yes. Less than 10kohms is failing. Some drives require much more than that to overcome a ground fault.
__________________
It's not all the variables I am most concerned with, it's the undiscovered constants. |
![]() |
![]() |
#3 |
Member
![]() ![]() Join Date: Oct 2018
Location: Leesville
Posts: 81
|
Seperated motor from power booted drive up and no fault. looks like im searching for a motor. Thanks OkiePc
|
![]() |
![]() |
#4 |
Member
|
VFDs are better at finding faults than a lot of other things that are supposed to...
|
![]() |
![]() |
#5 | |
Lifetime Supporting Member
|
Quote:
![]() That should read 10 megohms. I have seen motors on starters work as low as 2 Mohm. I once replaced an obsolete 1336 VFD with a Toshiba G7 and it wouldn't run. The motor megger test showed 80 Megohms to ground... The 1336 was fine with it, the G7 said nope.
__________________
It's not all the variables I am most concerned with, it's the undiscovered constants. |
|
![]() |
![]() |
Bookmarks |
Currently Active Users Viewing This Thread: 1 (0 members and 1 guests) | |
Thread Tools | |
Display Modes | |
|
|
![]() |
||||
Thread | Thread Starter | Forum | Replies | Last Post |
Abb acs550 pfc macro control | osama223 | LIVE PLC Questions And Answers | 2 | August 1st, 2017 10:51 AM |
ABB AC drive fault | mmgch | LIVE PLC Questions And Answers | 3 | August 7th, 2009 04:48 AM |
Generic fault finding methodology | Engineer1 | LIVE PLC Questions And Answers | 7 | July 16th, 2009 08:36 PM |
RSLogix User Fault Routine | jthornton | LIVE PLC Questions And Answers | 17 | October 23rd, 2008 03:55 PM |
Mitsubishi Still Sucks... | Eric Nelson | LIVE PLC Questions And Answers | 23 | January 15th, 2003 05:15 PM |