Old February 24th, 2004, 07:30 PM   #1
ltrail
Member
United States

ltrail is offline
 
Join Date: Sep 2003
Location: Pennsylvania
Posts: 25
Angry Siemens HMI TP070 Comm Problem

I'm hoping some of you experienced Siemens folk will help me on this one. I have a Siemens S7 224 and associated PPI/PC Cable for downloading the program to the S7. That works well. But when I connect the PPI/PC cable (its a USB connection at the PC), I get the following PC error message, "Could not establish connection. Please check your settings, interface cable, etc!" Another screen says, " Download Failed. Please check the following, 1) Cable connections between PC and TP, 2) Port number selected for comm between PC and TP (it is COM1 and 38400 baud rate), 3) TP is in the serial download mode before starting download
I'm hoping that someone has been here and done that; and has the answer. At first I was connected to a D-Link USB hub. But I recently tried directly to a USB port on the computer. Still nothing successful.

Thanks.
__________________
Siemens S7 200 Series Student
  Reply With Quote
Old February 25th, 2004, 01:36 AM   #2
GEOFRA
Member
Cyprus

GEOFRA is offline
 
Join Date: Jul 2002
Location: Nicosia
Posts: 99
TOP70

After you connect the PPI cable turn the TOP70 power off and then On again.There will come a menu on the HMI and select to establish a connection from the HMI.
  Reply With Quote
Old February 25th, 2004, 08:23 AM   #3
CT782
Member
United States

CT782 is offline
 
CT782's Avatar
 
Join Date: Jan 2004
Location: NC
Posts: 88
Go to your "Control Panel" for your PC and look under "Set PG/PC Interface". Make sure "PC/PPI Cable is selected" Then click on "Properties" In the "Properties" section under the "Local Connection" tab, which is the PC to Adapter connection, you must select "USB" if you have it set to COM1 the PC is looking for your PPI adapter on the serial port. Your adapter should have come with a driver disk, which once installed, will enable you to select the USB option if it's not there. Mine only gave me the option to select COM1 or COM2 until I installed the driver for the adapter.
__________________
Quote:
Before you attempt to beat the odds, be sure you could survive the odds beating you.
  Reply With Quote
Old February 25th, 2004, 08:21 PM   #4
ltrail
Member
United States

ltrail is offline
 
Join Date: Sep 2003
Location: Pennsylvania
Posts: 25
Angry Siemens TP070 HMI Comm Problem

Geofra. I tried turning off power to the HMI after connecting the USB/serial PPI/PC cable but it didn't help. After turning on and setting itself up, it automatically searches for host.

CT782, I checked the PC's Control Panel, Set PG/PC Interface and found that it was already set on "USB". As I mentioned, I have already used the PPI/PC cable to download to the S7 224 unit. What I did find, though, is that in the TP Designer application, under Setup/Communications/Options/Port, it shows only COM1 or COM2 options; no USB option. And it provides a bunch of baud rates that would be suitable for serial communications. I believe that my version 1.0 is the fault. Would anyone know whether USB has been added to upgrades of the program?
__________________
Siemens S7 200 Series Student
  Reply With Quote
Old February 25th, 2004, 09:21 PM   #5
charlesfan
Member
China

charlesfan is offline
 
Join Date: Jan 2003
Posts: 17
Which type cable in your hand?
USB->232 Adapter+ 232/PPI cable or USB/PPI cable?
  Reply With Quote
Old February 26th, 2004, 05:11 AM   #6
ltrail
Member
United States

ltrail is offline
 
Join Date: Sep 2003
Location: Pennsylvania
Posts: 25
Charlesfan. I have a USB-PPI cable. The cable works perfectly when downloading to S7 224. The computer properties says the cable is working properly.

The TP070 program does not give me USB option in communications, so I believe it's trying to transfer in serial mode at the default baud rate and port. I'm provided only two options for port in the program: COM1 and COM2. The program is called TP Designer, Version 1.0. When I am at the start screen, it shows "Start", "Transfer", and "Configure". After a few moments, the program automatically goes into "Transfer" but not successfully as I get error messages on "Result" page of application at my PC. Thanks.
__________________
Siemens S7 200 Series Student
  Reply With Quote
Old February 28th, 2004, 06:11 PM   #7
ltrail
Member
United States

ltrail is offline
 
Join Date: Sep 2003
Location: Pennsylvania
Posts: 25
I proffered the questions regarding USB and the TP070 HMI unit to Siemens. Here is the Siemens reply, "USB is not supported by TP Designer / TP070.
You need always a PC/PPI cable to project a TP070. Each version of PC/PPI cable is ok even the very old ones with only 4 dip switches. USB cable or any other cable is not compatible.

If you are no able to find a PC with a serial (COM) port the only chance may ba a USB/serial adapter. If the driver simulates a COM port, it may work. In TP Designer you config COM1 then and the conversion to USB is done by the driver of the adapter. But as this is not tested and ther are several different adapter, we canīt garantee this application. We recimmend the PC/PPI cable and a serial port in PC."

So I've learned that the USB type PPI/PC cord is supported by Siemens S7 224 but not the Siemens TP070 HMI (a low-end HMI unit that is on its way out of favor).

I ordered the correct serial-to-serial PPI/PC cable on Friday.

Would anyone know whether there are HMI's by Siemens or others that support USB and would work with the S7 224 PLC? Some day, I'd like to upgrade to a more sophisticated color unit that provides graphics capability.

Thanks for the help here at the site.
__________________
Siemens S7 200 Series Student
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
Siemens S7 Ethernet Problem S7Guy LIVE PLC Questions And Answers 7 February 4th, 2008 02:51 PM
TP070 Siemens Panel display - strange problem Preeya LIVE PLC Questions And Answers 4 January 15th, 2006 10:23 PM
HMI to Database alarms & comm problems philjf LIVE PLC Questions And Answers 0 April 8th, 2004 09:34 AM
I/O Comm. problem btw PLC & HMI WFox LIVE PLC Questions And Answers 7 December 31st, 2003 01:09 PM
S5 Siemens to HMI lambles LIVE PLC Questions And Answers 3 September 26th, 2003 04:42 AM


All times are GMT -5. The time now is 05:31 AM.


.