Old January 16th, 2015, 09:47 PM   #1
Bbarnett
Member
United States

Bbarnett is offline
 
Join Date: Jul 2013
Location: United States
Posts: 76
What is a Test Output on a Safety Relay?

I'm looking to use a Guardmaster Safety Relay from Allen Bradley. Its redundant input will be from the output of a GuardLogix PLC. That will work, right?

What's throwing me off is that the example connection diagrams for the Safety Relay show Estops connected to the Test Output which pulses. That's making me think that the safety input is looking for a pulsed signal.

Can somebody shed some light?
  Reply With Quote
Old January 17th, 2015, 12:51 AM   #2
sparkie
Lifetime Supporting Member
United States

sparkie is offline
 
Join Date: Nov 2014
Location: KS
Posts: 1,127
What specific safety relay are you using? These things can be tricky, we have them on our saws at work. They can go FM on us sometimes.
  Reply With Quote
Old January 17th, 2015, 04:17 AM   #3
Donnchadh
Lifetime Supporting Member
Ireland

Donnchadh is offline
 
Join Date: Jun 2002
Location: Ireland
Posts: 1,004
Hi

Sorry to ask but if you have a guard logix plc what is the need for a safety relay?
Would you not wire the items into the guard logix ?

Donnchadh
  Reply With Quote
Old January 17th, 2015, 06:36 AM   #4
Bbarnett
Member
United States

Bbarnett is offline
 
Join Date: Jul 2013
Location: United States
Posts: 76
Sparkie - None yet. I am thinking about ordering one if it is needed.

Donnchadh - That's what's racking my brain about this. The robot controller has a fence circuit that is currently being jumpered. Basically it has a +24V terminal that goes into a +IN terminal and a 0V terminal that goes into a -IN terminal. The GuardLogix gives me 2 redundant outputs.

I can only imagine that those two outputs with energize a coil that will open/close the contacts on the fence circuit.

We've used Interface Modules from Banner before, the IM-T-9A. I attached a schematic of that. I'm thinking that the GuardLogix only replaces the Primary Safety Device in that image. I am limited to only using Allen Bradley so that's why I can't just use the Banner Interface Module.

Can you think of a way around my thinking? Can I really just plug in the 4 wires from the fence circuit into the GuardLogix?
Attached Images
File Type: png IM-T-9A.PNG (33.2 KB, 98 views)
  Reply With Quote
Old January 17th, 2015, 07:57 AM   #5
dginbuffalo
Member
United States

dginbuffalo is offline
 
Join Date: Dec 2010
Location: Buffalo,NY
Posts: 630
Not sure what flavor Guardmaster your using, but I believe you are correct-the test outputs (S11 S12?) pulse in different sequence. This is to check shorts to +DC and wire to wire shorts.
  Reply With Quote
Old January 17th, 2015, 09:56 AM   #6
James Mcquade
Member
United States

James Mcquade is offline
 
Join Date: Oct 2007
Location: Nashville, Tennessee area
Posts: 3,546
Bbarnett,

if the robot circuit is jumpered meaning bypassed, then you should shut down the machine and fix the circuitry asap.

I don't know your system, but when you bypass a fence circuit guard on a robot, you are asking for trouble.

regards,
james
  Reply With Quote
Old January 17th, 2015, 12:13 PM   #7
Donnchadh
Lifetime Supporting Member
Ireland

Donnchadh is offline
 
Join Date: Jun 2002
Location: Ireland
Posts: 1,004
Hi

You could use a set of safety contractors using the outputs from the guard logic
I would also wire a edm back to the guard logic

Donnchadh
  Reply With Quote
Old January 17th, 2015, 05:38 PM   #8
rigicon
Member
United Kingdom

rigicon is offline
 
rigicon's Avatar
 
Join Date: Aug 2009
Location: kent
Posts: 415
A test output on a safety relay is a pulse output every say 200 ms to check there is no frigs on the circuit. Frigs=engineering bypass. You can choose if this option is active or not. The pulse is usually superimposed on the + 24VDC line and is only of short generation.
__________________
Artificial Intelligence - Genuine programmers headache

  Reply With Quote
Old January 18th, 2015, 02:53 PM   #9
Bbarnett
Member
United States

Bbarnett is offline
 
Join Date: Jul 2013
Location: United States
Posts: 76
Thanks everyone for all the helpful replies. The cell is in the beginning stages of design so no worries about safety issues yet. The robot controller comes with the safety fence bypassed.

I think I finally understand what I need. I got the OK to use the Banner interface modules since I'm most familiar with them. I will use them for the fence circuit and tie in a positive feedback EDM through the contactors.
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
controllogix relay output won't energize CABLETRAY LIVE PLC Questions And Answers 13 September 21st, 2017 08:41 PM
Trying to understand safety PLC's (specifically Siemens) Jieve LIVE PLC Questions And Answers 3 June 24th, 2014 09:27 AM
Estop relay question g.mccormick LIVE PLC Questions And Answers 6 December 6th, 2013 07:54 AM
Safety using Micrologix 1000/MSR210 safety relay dskplc LIVE PLC Questions And Answers 2 August 11th, 2013 03:30 PM
SLC500 Relay Output Module ceilingwalker LIVE PLC Questions And Answers 3 August 7th, 2012 04:58 PM


All times are GMT -4. The time now is 03:00 PM.


.