PLC5 PID triggering curiosity - confirm my thougths please
wildswing
May 2005
Sault Ste Marie, Ontario
281
Hey fellas,
This one's more of a curiosity than "gotta fix it now" kinda thing. I've just discovered some PID loops in one of our PLC5s that are triggered by pulse bit (ON for 100 and OFF for 100), not a single scan timer.dn XIC. The PID update times are set to 100 msec. The control is a PD file (not Integer). The PLC scan time varies from 20 - 50 msec.
I've read all the help files and a bunch of posts here, so I think I'm on the right track here. Just asking for confirmation if my thinking is right or not.
To me that's programmed wrong. With the control being a PD file (not N), the PID instruction will execute 2 to 5 times when the trigger pulse is ON, then lie quite while it's trigger is OFF. With the update time set to 100 msec, the Ki (no Kd) will act 2 - 5 times more often than expected, thus to achive acceptable tuning, it's value is most likely 2 - 5 times lower than it would be if the PID were being triggered properly.
To be correct, these PIDs should at least be triggered by a timer.dn xic that's true for only one scan. Better yet, they should be in a 100 msec STI file.
Looks to me that the original programmer thought the PIDs would only execute on the false to true rung transition, not every scan, or he thought the PD worked like an N file control with a .DN bit. This has most likely been this way since day one of the OEM setup many moons ago so I'm not in a rush to fix it.
Yes, I agree with you. I have seen situation like yours where what I thought were the right tuning numbers to change when I fixed ended up being wrong, and then I ended up having to adjust some other settings (VFD ramp rates in my case) to get back to acceptable control, but once that was done, the performance and the ability to fine tune was improved immensely.
If there is any integral gain, I think you may see a sharp difference in performance when you make it right.
wildswing,
The behavior of the PLC5 PID may be unpredictable in your case. I've only seen and used PLC5 PID's with the xic.dn of a free running timer to trigger and always move the .pre of the time into the PID to ensure the correct update time is being used. Which I know will cause issues.
Cheers
Has anyone had an issue with a PID control after the processor has been upgraded form a L40E to a L80E. It does not seem to be controlling...
48
6,003
I am working on a PLC5 that is doing temp control. However the temp control is working more like ON/OFF and not Proportional control. I am not...
32
8,585
Has anyone ever converted a the PID instruction from a PLC5 to a CLX platform? The issue I am facing concerns the difference between a PID...
3,462
I'm working on a project to convert an old PLC5 processor to an L63. Below is sample logic of one of the several PID controls from the...
5,040
Hey fellas, I'm in the midst of doing my first translation from 5 to 5000 that also includes PID instructions. I'm just looking for any helpful...
5,483