OMRON Program Upload Issue
SouthPahw
Mar 2011
Heartland U.S.A.
25
I posted this on a reply in another thread, but with now responce thought I should seperate the issue.
Info: I am using Syswin, have the correct Cable and Host Links.
I have succesfully uploaded two different programs from C20 units.
Problem is with:
● OMRON C200H CPU01 C200H-ME831 Memory Unit EER-ROM 16kb
Using C200H-LK201 host link unit.
I can get on-line and connected; But I can not upload program.
I have gone thru manuals and tried every C200 option in Syswin.
It will start upload; then get a message:
"Command Not supported in Current PLC
You may have the wrong PLC Type"
As I said, I tried all the C200 options. I can Change the PLC Modes with no problem.
The only thing I even found close in manual was really applicable to downloading programs, but It said some C200H's had to have the I/O configured.
So I set up the off-line program with the current PLC I/O and C200H in project setup. Same issue.
Any suggestions? What am I missing?
Thanks.
How are the switches set on the HostLink?
There are rotary switches on the front and 4 dip switches on the back.
Not sure it that is the problem, but it is a start.
On Front: Switches 1, 2, & 4 = 0 and Switch 3 = #5 (9,600 bps)
On Back: Switches 1, 2, & 4 = OFF and Switch 3 = ON
CTS Setting, was OFF, relooked at layout and tried ON position.
Did not make any difference, same message.
And could still change modes from Run to Off with no issues.
But can not upload program. Still looking and listening...
Thanks!
if you are connected can you toggle the program between stop and run?
Based on the information in the manual W143, front Switch #4 should be set to 2. This sets the command level to "1,2 & 3".
A zero setting is command level "1".
Command Level 2 allows Program Read and Program Write.
Command Level 3 allows for Compound Commands.
Try changing Front Switch to 2 and that should solve the problem.
Hope this will help.
Hello everyone. I am new when it comes to Omron PLCs. Currently I'm uploading program from CJ1M PLC using CS1W-CIF31 cable only. I connected the...
135
We want to upload program the following PLC, and downloading to Our Spare. And also we want keep program in file . Could You give quotation for...
1,218
Dear Friends; We have OMRON CJ1M CPU23 with I/O cards at one of our machine. We have arranged a spare PLC and tried to download the program...
6,900
instructions Upload Program PLC Omron CPM1A to PC for people starting go to view instructions Upload Program PLC CPM1A please you selection a...
3,380
Hi all. I've found myself, once again, walking into a situation where there's already poop on the fan blades. Long story short, I have an Omron...
7,544