ML1100 to ML1400
RMore
Dec 2011
Kenmore, NY
64
I have a program written for the ML1100 that I must get to work in a ML1400 (apparently, the ML1000 is reaching end of life soon).
When I change the processor from ML1100 to ML1400, I immediately get errors relating to the OSR function due to the difference ways the two PLCs handle the OSR function. Can someone explain the difference? What do I need to do to replace the OSR fucntion on he ML1100 with the OSR function on the ML1400?
The rung on the ML1100 version is currently as follows:
T4:20 B3:2
|---[OSR]-------------(L)---------|
DN 15
Also, is there a document that explains what needs to be considered when migrating from ML1000 to ML1400?
That's news to me. The standard instruction set should be the same. What's the error? Also, make sure the data-table matches.
RMore,
From the title down, your post is littered with incorrect references to the "ML1100" instead of the "ML1000". This is somewhat confusing to readers trying to help you. The only way to be sure which you meant was to know that the OSR works differently in the MicroLogix 1000 to all the others. Just try to double-check your posts in future, if you can.
gbradley said:
Try changing your OSR to ONS.
That will do it. The ONS in the other MicroLogix controllers is the equivalent to the OSR in the MicroLogix 1000.
Seeing as you are converting an entire program this should prove helpful in your quest...
719811 - MicroLogix 1000: Instructions that don't convert from MicroLogix 1000 to other MicroLogix controllers
Access Level: Everyone
Regards,
George
As stated above they should be the same.
Your example is not an "OSR" instruction for a ML1100. Could be a ML1000 or a SLC500
The OSR instruction for the MicroLogix 1100/1400 does not
provide the same functionality as the OSR instruction for
the MicroLogix 1000 and SLC 500 controllers. For the
same functionality as the OSR instruction for the
MicroLogix 1000 and SLC 500 controllers, use the ONS
instruction.
TIP The ONS instruction for the MicroLogix 1400 provides the same
functionality as the OSR instruction for the MicroLogix 1000 and
Edit: Geospark types faster then I do and a whole lot better explanation.
ML1100 is actually ML1000
Geospark, Thanks for correcting my error. It is, in fact a ML1000 that I am converting.
Also thanks for the link. Very helpful.
RMore,
I'm looking to implement a low-cost, efficient method of communicating some integer values to an R30iB robot from a Rockwell 1100 PLC. I am not...
1,723
Hello all, I am trying to setup my MicroLogix 1100 as a modbus RTU master for a modbus network containing multiple modbus RTU slaves. I currently...
3,916
We have a machine that keeps losing its program at random intervals; sometimes 2x-3x in a shift, sometimes will go over 1wk without issue. I had a...
2,932
Just asking for clarification here, but from my research all I need is a 500 ohm resistor across the AI and the common? Heres my schematic. I...
2,579
I have a CLX L61 and I'm trying to read from and write to a Micrologix 1100. I'm attempting to read 200 REAL elements but I'm receiving an error...
1,458