FactoryTalk View and KepServer Modbus Addressing Syntax
elmatador
May 2008
Canada
108
Hi Guys,
I am creating Factory Talk View Tags (RSView). I want to tie these tags directly to kepserver without having to declare a seperate tag in the Kepserver. Let me give you an example.
I have a modbus address of 44160. In the HMI Tag, I want to tie it to the following topic
Scadapack.Scadapack357.44160@long
Using this value I am supposed to be able to tie the tag without have to declare another tag in Kepserver. But this is not working for me. Has anyone used this format before?
It sounds like you are using DDE & not opc, in opc you only need declare the channel & Device in kepware but then in the client you need the actual address i.e.
Kep = Channel1.Device1
Client Channel1.Device1.M100
I have nuisance alarm that comes and goes. Doesn't seem to stay longer for a few seconds, is there any way I can somehow add a time delay or...
1,503
In the plant I work in we deal with a lot of the old TI-545 PLC's I have since been interfacing them with ethernet cards and adding Panel View...
5,625
Hello, I'm using FactoryTalk View ME V10. I created a valve as a global object with multiple parameters and when the object is being used at the...
129
Hello all, I was modifying an HMI in factory talk and went to change a go to display button using the ... to select from a list as I had done...
168
Hello, We recently upgraded our control server to a newer model. After the transition we are experiencing issues with our trend graphs to where...
120