1761-NET-AIC and MicroLogix1400

GPS

Member
Join Date
Aug 2016
Location
Melbourne
Posts
4
I have a bunch of ML1000 PLCs on a DH485 network using 1761-NET-AIC modules and we are replacing the ML1000s with ML1400s.

Once all of the ML1100s are replaced with ML1400s we will replace the master PLC and the comms will be via Ethernet but in order to stage the replacements, we need the ML1400s to temporarily communicate via DH485.

My question is:

Can I simply plug the mini DIN plug from the AIC into the ML1400 or do I need to use a 1763-NC01 in order to connect the DH485? At present the AIC is powered from the ML1000 so obviously I will need to provide an external power source.

Further, if I must use the 1763-NC01, will the phoenix connector that is in the AIC module fit straight into the NC01?

Unfortunately this is an operating plant so I need to have as much information up front as possible.
 
Page 83 talks about using the 1763-NC01 with MicroLogix 1100's.
Having said that the pin out for all of the mini din ports is the same when it comes to communications (careful with power) so I'm not sure why you couldn't just set the MicroLogix 1400's port up to be DH485 and go from there.
 
Page 83 talks about using the 1763-NC01 with MicroLogix 1100's.
Having said that the pin out for all of the mini din ports is the same when it comes to communications (careful with power) so I'm not sure why you couldn't just set the MicroLogix 1400's port up to be DH485 and go from there.

You are right that should work.

The only difference is the ML1000 can provide power for the AIC ( pins 1 and 8). The ML1400 cannot. As the OP said power will have to come from an external 24 VDC power supply.
 
Page 83 talks about using the 1763-NC01 with MicroLogix 1100's.
Having said that the pin out for all of the mini din ports is the same when it comes to communications (careful with power) so I'm not sure why you couldn't just set the MicroLogix 1400's port up to be DH485 and go from there.

Thanks to you both for your responses.

To Firejo, page 83 of what?
 

Similar Topics

Hello, currently I have a micrologix 1200 (1762-L40AWAR )connected to an HMI panelview 600(2711-T6C3L1X) via the 1761-net-aic module, I want to...
Replies
13
Views
1,770
I've attached pics, below. I'm in the field right now an am trying to communicate to the Micrologix 1500 through the 1761-NET-AIC (Ugh!) to...
Replies
6
Views
1,935
The manual for the 1761-NET-AIC shows connecting a PC to DH485 network with a 1761-PM-02 cable. Is this done using a DF1 driver set to...
Replies
0
Views
1,055
A customer of mine has a ML 1500 LRP connected to a Net-AIC+ via the mini din connector (CH 0 of plc to port 2 of AIC) from this AIC then connects...
Replies
3
Views
1,778
Hello everyone, I need to adjust some timers online with a SLC503 that has both channels used. Channel 0 is configured for RS422 and is connected...
Replies
9
Views
4,157
Back
Top Bottom