TIA Portal and SFB52/53

Michal_dk

Member
Join Date
Oct 2007
Location
Vejen
Posts
153
Has anyone here had success with reading or writing parameters directly to a device using the SFB 52 or 53 blocks in TIA portal?

My problem seems to be in the address, if I set up a system in S7 Manager and a 300 CPU I have no problem. I use the "Diagnostic Address" of the device as the address on the SFB and communication works.

On the TIA portal I can't find the "Diagnostic Address" But I have the "HW Identifier", but using this I get an error everytime I activate the SFB.

I have tried searching the web but have until now come up short on an example that involved TIA.

I have TIA 11 and TIA 12 at my disposal.
 
Hmm, it would seem that the HW Identifier IS the address to use, but I get a status Word like this:
C089_3A00

C0 means "No DPV1 protocol element is used", but what does it really mean?

I'm using PPO type 5, so I think I'm using the right communication type?

Oh, and SFB 52/53 is RDREC and WRREC
 
Last edited:

Similar Topics

Im trying to create a level indicator for water Tank i have used the ADD function while the pump is on and level increasing everything works...
Replies
17
Views
126
My PLC (S7-1200 with CPU-1212C) has now been delivered to customer site. They've asked me to do some updates to the software. I can do that on my...
Replies
21
Views
330
Does anyone know why the connection interface is greyed out and says why I can only use Teleservice instead of the other options like PN/IE? I am...
Replies
0
Views
44
Hi guys I after a bit of advice on Tia portal graphics, I would like to add a conveyor belt graphic to a hmi and the conveyor in the basic...
Replies
3
Views
130
Hi I used to be able to launch PLCsim without any problem. Now it tells me " STEP 7 Professional Licence is required to simulate this PLC"...
Replies
15
Views
453
Back
Top Bottom