Do I need a feedback card to acquire motor RPM from a VFD?
belae1ka
Nov 2016
mt pleasant, mi
The VFD I plan on using;
DURApulse GS3 series AC drive: https://www.automationdirect.com/static/specs/gs3drives.pdf
Model: GS3-22P0
The feedback card accessory for the VFD: https://www.automationdirect.com/static/specs/gs3fb.pdf
Hi everyone, I would like to know if I need this feedback card to obtain RPM of a motor that is being wired using the VFD specified above. I plan on controlling a 3 phase motor with the program Labview. I will be using MODBUS to communicate between the VFD and Labview.
The end goal of my project is to plot the force of a load cell with respect to an increasing motor RPM so I was wondering how to get the RPM feedback from the motor. What exactly is the main purpose of this feedback card? In what kind of applications would this card be needed?
Model: GS3-22P0
If accuracy was not critical, you could simply infer motor RPM based upon the speed reference value being sent to the drive. The option module offers an implied measurement based upon the drive output frequency, but if the RPM data was absolutely critical, then I would employ a tachometer.
The feedback card is to wire a shaft mounted encoder back to the vfd. This will serve as the feedback for the vfd speed control. Without an encoer, the vfd should control shaft speed to within a fedw rpm. With encoder feedback, the vfd should be controlling speed to within 0.5 rpm.
If you are reading/writing values via modbus, you should get motor speed regardless of if the vfd had feedback or not.
For the GS3 drive.
Write value for requeste hz = Register 2331 (integer)
Read motor RPM = Register 8456 (integer)
For the GS3 drive.
I must admit that I was guilty of assuming that the feedback card simply offered implied motor speed information calculated by the drive. An encoder input is an actual tachometer.
I am looking for different solution on controlling a pneumatic Cylinder move at preset positions. One of the solutions is to use 5 magnetic...
22
5,973
Good Morning, I want to install RS Logix 5000 v.20.04 on a laptop that has 20.01 on it already. I've figured out that I do not need to update...
3,352
Hi all sifu, I'm facing a problem recently when trying to retrieve the atv61 drive current feedback via its AO1 output in mA when the drive is in...
2,590
help me please :shoot: :shoot: i need full project on s7 1200 of feedback elevator 34-150 plz plz i need it soon and thnnx 📚 :D
4,261
I want to have some feedback about the MESInterface IT from Mitsubishi. I have never use mitsubishi stuff and we might merge to them. I read...
2,579