Hello everyone...

I'm facing one problem on recently purchase the PanelView Plus 700(Cat.Log 2711P-T7C4A8, SER A). FactoryTalk View ME Ver 9.00, *.mer ver 9.0(I tried in V5.1, V7.0, V8.0, and V9.0) RSLinx Ver 3.81.

Error "The Destination selected is not a valid device. Please select the Valid destination and try again"

I face this problem if we use ME transfer Utility for PanelView 800 Device. That's acceptable.

Please help me...

Thanks in advance

1.jpg 2.jpg
 
Have you tired to transfer the .MER with a CF or USB?


Are you sure that the new PV is 9.0 and not 10.0?


If it is try deleting the driver in Linx enterprise and build a new one.


If you have Tech Connect support search 24344 and 276779
 
Have you tired to transfer the .MER with a CF or USB?


Are you sure that the new PV is 9.0 and not 10.0?


If it is try deleting the driver in Linx enterprise and build a new one.


If you have Tech Connect support search 24344 and 276779

Yesterday I downloaded with USB only...
If your asking for PanelView Versions then its showing 10.
 
I think the version may be wrong there is 2 ways to fund the version ,
1) on boot up the hmi shows the version as app (9.0app) would be verion 9

2 go into config screen -teminal settings- system info-about factorytalk
Then create a runtime to that version ?
 
I think the version may be wrong there is 2 ways to fund the version ,
1) on boot up the hmi shows the version as app (9.0app) would be verion 9

2 go into config screen -teminal settings- system info-about factorytalk
Then create a runtime to that version ?

HMI Version is 10..
I transfer the file with USB and its working good..


I think version is not an issue because we can make a .mer file with lower version.. Of it's creating a problem then after download error have to incompatible version...
Some HMI's have v8 and lesstgen that version .Mer file runs fine..
 

Similar Topics

My Panelview plus 700 HMI stopped working and I replaced it with a new one. Moved the sd card from the previously installed panel to this one and...
Replies
16
Views
989
Good day all! I need to make some modifications to a Panelview program. I uploaded it from the unit. Tried to use the Application mgr. to...
Replies
6
Views
1,090
Hi All. I am working on my home automation system again and i am looking at setting up a panelview. Currently running an AB Compactlogix...
Replies
3
Views
839
Hi. I'm working on a plant that has a panelview plus 700. Problem is that from time to time, the alarm list shows an old false alarm instead of...
Replies
10
Views
2,720
Back
Top Bottom