Hi,

We will add a few devicenet networks to some PLC5 systems in April. About 30 valves and 10 drives approx per network.

I don't have the exact spec for each plant controller only that it's PLC5. Can I assume the 1771-SDN will work with all variants of PLC5 and go ahead and order or something to watch for?

Thanks
 
A few things
You will need RSNetworks for devicenet to set them up
Devicenet has a limit to the number of nodes per network I think it's 64 you should check on that before you start, you may have to add a devicenet module.
 
A few things
You will need RSNetworks for devicenet to set them up
Devicenet has a limit to the number of nodes per network I think it's 64 you should check on that before you start, you may have to add a devicenet module.

No problems with software or configuring the SDN, done it many times. Just need to know if there are variants of PLC5 that don't support the SDN.
 
A few things
You will need RSNetworks for devicenet to set them up
Devicenet has a limit to the number of nodes per network I think it's 64 you should check on that before you start, you may have to add a devicenet module.

The 1771-SDN is the DeviceNet Module!
 
A few things
You will need RSNetworks for devicenet to set them up
Devicenet has a limit to the number of nodes per network I think it's 64 you should check on that before you start, you may have to add a devicenet module.

The theoretical limit is 64 nodes (0-63) but I believe the general consensus is not going over 40 or so. You start to have problems if you crowd the network too much.
 

Similar Topics

I am using the following formula and I am getting error, Invalid Expression - too many closing parenthesis. when i copy the formula to notepad or...
Replies
4
Views
152
Preface: Kinda long, so I made section titles Intro: I just want to see if anyone here has seen anything similar. A PLC5-40 series C enhanced...
Replies
3
Views
365
Hi, can anyone help me get a pdf file for this RSP files. They are from a PLC5. Thanks
Replies
5
Views
517
Hello all, I am seeing this behaviour where an integer file (N46:33), has an integer in binary (11110) which is 30 in decimal. I did a...
Replies
7
Views
516
Back
Top Bottom