Modbus micologix 1400

Hojland

Member
Join Date
Oct 2006
Location
Langå
Posts
203
Dos anyone have an rss file(logix 500) with modbus rtu communication. I am trying to get some value out of an janitza ugm511 power analyser. Eg modbus adress 19000 voltage L1-N
 
Thanks harryting😀 I have seen that. But I dont know how to setup up the MSG funktion for modbus. That is why I was hoping some one had don it before
 
Backup a bit, you are setting up the 1400 as Master, right?

Check out the Rockwell SCADA Application manual: ag-um008_-en-p.pdf

Start on page 3-57 it shows how you config MSG.
 
I didt that in the begining, but all the example that I have seen, the set the ML1400 as slave. Hmm dont get it.
 
Example is just that, in YOUR case, you need to figure out which should be the master and which one is the slave. ML1400 can be either but a lot of lower functioning device can only be slave so the decision is made in such cases.

It's not clear in your post that you setup the physical layer stuff already, have you done that yet and have you tested it with some other device or PC based modbus simulator?
 
It is my first time, doing modbus. That is way I was asking for an example rss file or an guide. I will try on again on monday. Thanks
 
I got your mail. Thanks. I will look at it on monday. Can I just use a straight throu cabel from ML1400s sub d (channel 2) to janitza sub d?
 
The ML1400 channel 2 doesn't support RS485 - only RS232. The easiest solution (but some say not the cheapest!) is to use the Allen Bradley 1763-NC01 (see attached). This provides a break-out termination block to connect your Modbus A & B lines as necessary.

I also have a library of RSLogix500 files for both Modbus Master & Slave if it is of any use to you?

Regards,

Rob
 
I don't have a sample with me, but one thing you absolutely MUST do is power-cycle the PLC after you change the chanel configuration. I once wasted an entire day trying to establish modbus comms until I tried a reboot on a whim.

I'll send a sample in the morning
 

Similar Topics

I have a PH meter that I am trying to bring its data into 1756-L81. I have downloaded the Rockwell MODBUS AOI kit, but I am not sure if I need to...
Replies
0
Views
24
Dear All, i am trying to connect Danfoss inverter with s7 200 cpu 226.but microwin shows following error at DATA Ptr.i assigned different VB...
Replies
1
Views
38
I'm trying to control a device via MODBUS RTU and the ModbusRtuMasterV2_PcCOM in Twincat 3. I've configured a device with the right com port and...
Replies
6
Views
124
Hi all, Currently having trouble getting a speed reference to write over modbus to an Omron M1... I can successfully write a run command and...
Replies
6
Views
206
Apologies for not being the best IDEC programmer. I recently was doing some inspections on a site that had 3 FC6A IDEC processors. The issue is...
Replies
0
Views
72
Back
Top Bottom