Panelview Plus Alarm Screen Question

asmaint2

Supporting Member
Join Date
Jul 2009
Location
Defiance, Ohio
Posts
31
I have a Panelview Plus 1000, 2711P-T10C4D1, the logic module is a 2711P-RDT10C, 5.10, and I using Factory Talk View Studio 6.10.
I was using the standard alarm banner to view and acknowledge alarms. The operator could acknowledge the alarm and close the screen. I also had an alarm history screen that could be called for maintenance purposes. One of the maintenance personnel found that if the alarm history screen was being viewed and an alarm became active, therefore calling the alarm banner, you were not able close out of both screens. The alarm would acknowledge, but pressing either close screen button would only toggle you between the alarm history and the alarm banner. I have since removed the alarm history screen and also removed the acknowledge button from the banner. We can can call the alarm banner from a "Maintenance Only" screen to see the list of alarms if neccessary. Everything is working now, I was just curious if there was a fix to what we discovered.

thanks,
 
I need to make a correction to my thread. I was not using the default alarm banner, I was using an alarm list. If the alarm history screen was open and an alarm triggered the alarm list to display, the close button would only toggle between the two screens.
 

Similar Topics

Hello, I made a change in alarm setup in factory view studio, where I changed a alarm message text. After that I made a run application and...
Replies
0
Views
68
Hello, I have followed the "On_board Audit Demo" sample in FactoryTalk View Studio ME to add the functionality of exporting the Audit, Alarm, and...
Replies
3
Views
1,082
PanelView Plus 7 Perf I would like to upload the fault history from the panel to the PC, if it is possible to transfer the file to CSV format or...
Replies
0
Views
776
First time using a panelview. I have all of my alarms mapped to bits of dints. How do I get the alarm panel to popup when an alarm happens...
Replies
6
Views
2,072
I use PanelView Plus 7 Graphic Terminals Model: 2711P-T10C22D8S-B PLC: Compact Logic 1769-L36ERM Tag ER[4].8 -> ON, the message is "1046 Abnormal...
Replies
1
Views
1,720
Back
Top Bottom