how to wire analog sensor to PLC
mikeecbr
Jan 2018
Chicago
If I'm reading the cutsheet correctly, Brown goes to +24VDC, blue to (-) terminal on plc input and black to (+) terminal on PLC. If that doesn't get you where you want to be let us know.
Hi Webhead,
I don't quiet understand what you mean by (-) terminal on plc input and black to (+) terminal on PLC. I don't know how to wire up whole analog implemented i/o module. Please see attached.
Assuming you have no other analog devices connected;
You want to use diagram 3 on the ultrasonic sensor.
Brown +24v from power supply
Blue 0v from power supply
Black "I in 0+" on the PLC
You'll need to also have a short jumper on "I in 0+" and "V in 0+" to bond them. Lastly, you'll need to run a connection from the 0v connected to the blue wire of your sensor to to "V/I in 0-" on your sensor. This is on the bottom of page 184 in the manual you linked to.
Basically blue and brown on your sensor are to power the sensor. Black is your +mA output from the sensor. But it's a 3 wire sensor, so the 0v (blue) does "double duty" both powering the sensor as well as providing a reference to the controller.
An analog Transmitter (Sensor) with 2 wire and 4 to 20 mA output, is connected to an analog input module. The sensor requires an external 24 vdc...
2,160
Hi, Is it possible to connect 2-wire sensor and 4-wire sensor together in an analog module of a PLC, where COM terminal is only one single. For...
20
16,405
Hey folks, Hardware: *=Must use these devices. Allen Bradley 1734-AENTR (Dual Ethernet Adapter)* Allen Bradley 1734-IE8C (8Ch Analog Input...
691
Hi, Calculation of voltage drop of a 2 wire transmitter connected to plc AI is pretty simple and straight forward. My Question is could you...
2,096
Hi all! Silly question, I think.. Sitting here, drawing up a project, that receives 4pc 4..20 mA signals from another location. They say that...
1,460