RSLogix 500 Analog Output Maximum

pct_jimmy

Member
Join Date
Dec 2006
Location
Shady Spring, WV
Posts
61
Its been a while since I've programmed a SLC and I'm a little stumped about trying to find an easy way to do this. I am running a SLC 5/04 with a 1746-NIO4I analog IO module and I need to limit the maximum value of the output. The input is a pot switch and there is a selector switch that is intended to limit the maximum speed produced by a hydraulic valve/motor combo (position 1 is a lower speed, position 2 will allow a little faster).
I know there's a simple way to do this but I'm trying to get out of my foggy RSLogix 5000 programming ways and go backwards a little bit.

Any help is appreciated.
 
Wherever you are moving the data into the AO integer output simply have a greater than X move X into the output integer rung.
 

Similar Topics

Hello all. I have been working with an SLC 5/04 system, which houses various Digital and Analog INs and OUTs, up to Slot 29. I am currently...
Replies
3
Views
2,503
Hello guys, Hopefully a simple one for you but I can't seem to find the answer listed in Rockwell's literature...
Replies
3
Views
2,722
G'day lads, We are using an Allen Bradley PLC slc5/03 with an analog input module 1746 ni4. we have a sensor with a response rate of 250ms. in...
Replies
3
Views
3,135
I've got a slc 5/03 and the 1746-FIO4V card= 2 Input (V or mA) and 2 output (0-10 vdc) and am setting up an analog output in RSLogix. If so, I...
Replies
7
Views
9,614
hi! can anyone describe how addresing analog inputs in ladder diagram for RsLogix 500 and which symbol use?? i am new in RsLogix, till now i was...
Replies
3
Views
7,785
Back
Top Bottom