Intouch 10 slow to 555 PLC

Goku

Member
Join Date
Feb 2007
Location
Randburg
Posts
5
Hi, I've got a problem.

Got two 555-1106 PLC's connected with two 2572 ethernet cards to a CTI industrial switch. From there the ethernet goes to two Intouch 10 PC's.
The update to the PC's is very slow(5- 15 secondes). Sometimes when you start a motor on the one PC the running indication on the other PC will indicate and after e few seconds the used PC will only indicate.
I use CTI2572 IO Server and defined two topics. Each PLC with its own IP address. Should the Ports on the two PC's be the same or different? (Port number: 1505) At the moment it's the same.
The idea is to use the two topics in the redundancy of the Intouch.

The funny thing is that on my laptop I set up the same system on Intouch 9.5 and the update is fast!

Why? Ports? Intouch 10? Wrong IO Server Setup?
 

Similar Topics

Hi. Importing a 2014 aapck in 2023: no problem using it, adding windows, works very well, no problem whatsoever. Creating a new project: as...
Replies
2
Views
708
Hi, everyone I'm working with Wonderware System Platform and the InTouch applicaction is very slow. The graphics and the windows load really...
Replies
2
Views
4,000
Hello, please help me. I have big problem with communication between DASSIdirect 3 SP1 and S7-417H. I communicate over 5500 tags. There is VERY...
Replies
1
Views
3,798
Hi , i am converting a standalone app to a modern app with many archestra grapchics replacing the old classic ones.. . The thing is that each time...
Replies
2
Views
2,178
Hello and welcome to intouch people, These days I am having problem with fetching trends in Intouch very slow...I don't know where to...
Replies
3
Views
8,797
Back
Top Bottom