SLC5/05 IO TimeOut Reading

We are having an issue with a SLC5/05 timing out reading from the IOs on the backplane. Very briefly the setup is, 1747-L551 (SLC5/05), with 1746-IA16, -OW16, -NI4 (x2), and -NO41, with a PVP1000 as an HMI. Issue started a month or so ago with the original PLC, "Timeout reading N15:0 from SLC... Timeout reading from O0:0 from SLC... Timeout reading from T4:10-T4:11 from SLC... list goes on." We replaced the PLC, first time different rev/series number, and bad data tables, ended up PLC ran for maybe a day and then was completely incommunicable; tried battery reset, etc. nothing, but whatever. We replaced with another PLC with rev/ser no. closer to the existing, installed, programmed, and has been working well for close to a month now. Until last night, we received the same timeout alerts. In the past a reboot would reset the condition and the machine would run for 1-2hrs, I am assuming that holds true today but I have not verified yet this morning.



We added a PID block to control the speed of a pump several months ago but I would have thought if that were an issue it would have cropped up sooner, as we had a math error due to an infinite loop from the PID that we resolved with a reset block, can provide specifics if needed but don't recall offhand. That was in Feb 2018. Timeout issue started in early-mid May '18.


Any help would be appreciated, thanks!


Jeremy
  Reply With Quote
Old June 13th, 2018, 06:27 AM   #2
geniusintraining
Lifetime Supporting Member + Moderator
United States

geniusintraining is offline
 
geniusintraining's Avatar
 
Join Date: Jun 2005
Location: SC
Posts: 5,559
Quote:
In the past a reboot would reset the condition and the machine would run for 1-2hrs

Jeremy,

Have you done a full reset of the PLC and not just a 'reboot' and how much memory are you using? im just guessing but maybe you are running out of memory and need to go up to a L552

Are you storing a lot of data in the PLC ?
__________________
www.PLCCable.com PLC Communication Cables, PLC Trainers, Fluke Meters, MicroLogix, ControlLogix, Siemens, Allen Bradley and more... all your automation needs... ((NEW)) After Market 1784-U2DHP Allen Bradley USB to DH+ and Gateways
  Reply With Quote
Old June 13th, 2018, 06:28 AM   #3
janner_10
Supporting Member
United Kingdom

janner_10 is offline
 
Join Date: Dec 2014
Location: Tewkesbury
Posts: 622
I would change the backplane first. Low hanging fruit etc.
  Reply With Quote
Old June 13th, 2018, 06:58 AM   #4
Ron Beaufort
Lifetime Supporting Member
United States

Ron Beaufort is offline
 
Ron Beaufort's Avatar
 
Join Date: Jul 2002
Location: Charleston, SC
Posts: 5,412
make SURE that the chassis is PROPERLY grounded ...
__________________

2-B ?
Best regards, ----+----] [----+------------( )----
Ron | |
PLC Training Boot Camp | 2-B |
+----]/[----+

I once was lost, but now am found, was blind, but now I see.

  Reply With Quote
Old June 13th, 2018, 07:06 AM   #5
Aabeck
Member
United States

Aabeck is offline
 
Aabeck's Avatar
 
Join Date: Feb 2013
Location: Detroit
Posts: 968
Are those faults showing as major faults in RSLogix or showing on the HMI?

"Timeout reading N15:0 from SLC... " is a read from the SLC's memory, as if the HMI is timing out reading from the SLC.
__________________
Never underestimate the quality of idiots that will be running your machines
http://aabeck.com
  Reply With Quote
Old June 13th, 2018, 08:56 AM   #6
jfrye
Member
United States

jfrye is offline
 
Join Date: Oct 2017
Location: Charleston
Posts: 7
We replaced the back plane, and checked the memory: Memory used 582 ins. words used - 1076 data table; 11706 ins. words left. We found a resistor scorched on the power supply in the process, we replaced this with a refurb edition. Grounding to chassis and power supply.



The HMI and PLC are ethernet connected via a switch, the HMI has been replaced in the past, both ethernet cables have been replaced, and the switch has been bypass i.e. direct PLC to HMI connection; same results. This bit of work was done during the first occurrence in May,the replacement of the PLC is the step we determined to have resolved the issue at least temporarily.


We have not done a full reset on the CPU. We could reset the original CPU that had the issue and try it, but I kind of hate to do that because it is a spare that will at least allow my operators to wash down the machine. This is on a rotary drum thickener in a wastewater treatment plant, so when it fails it makes a horrible mess.
  Reply With Quote
Old June 13th, 2018, 09:12 AM   #7
rdrast
Lifetime Supporting Member
United States

rdrast is offline
 
rdrast's Avatar
 
Join Date: Apr 2003
Location: South Carolina Lowcountry
Posts: 5,215
Quote:
Originally Posted by Aabeck View Post
Are those faults showing as major faults in RSLogix or showing on the HMI?

"Timeout reading N15:0 from SLC... " is a read from the SLC's memory, as if the HMI is timing out reading from the SLC.

^^^ This.


This has nothing to do with your rack, it is a communications fault between the PLC CPU and the HMI. That is all it is.


I'm actually surprised that you can even read the output and input images directly, I haven't used an SLC is a long time, but I seem to remember that the I and O image tables can't usually be read by most communications software.
__________________
------------------------------------
How to ask questions the SMART Way!

Look First, Ask Second!

  Reply With Quote
Old June 13th, 2018, 09:35 AM   #8
geniusintraining
Lifetime Supporting Member + Moderator
United States

geniusintraining is offline
 
geniusintraining's Avatar
 
Join Date: Jun 2005
Location: SC
Posts: 5,559
Quote:
Originally Posted by jfrye View Post

We have not done a full reset on the CPU. We could reset the original CPU that had the issue and try it, but I kind of hate to do that because it is a spare that will at least allow my operators to wash down the machine. .
I would reset the PLC then reload the program... maybe swap them out so they have a 'working' PLC

Any chance you have noise on your ethernet cable(s) or a issue with the switch causing your timeouts ?
__________________
www.PLCCable.com PLC Communication Cables, PLC Trainers, Fluke Meters, MicroLogix, ControlLogix, Siemens, Allen Bradley and more... all your automation needs... ((NEW)) After Market 1784-U2DHP Allen Bradley USB to DH+ and Gateways
  Reply With Quote
Old June 13th, 2018, 09:40 AM   #9
Aabeck
Member
United States

Aabeck is offline
 
Aabeck's Avatar
 
Join Date: Feb 2013
Location: Detroit
Posts: 968
Quote:
Originally Posted by rdrast View Post
I'm actually surprised that you can even read the output and input images directly, I haven't used an SLC is a long time, but I seem to remember that the I and O image tables can't usually be read by most communications software.
I have had problems, and there have been more than one thread here, about problems with a HMI reading SLC I/O directly.

I always do a mirroring of all digital I/O to a B19: file and have the HMI check there instead of the I:1 and O:0 files. Also if direct reads of analog I/O is read I mirror those to an integer file for the HMI
__________________
Never underestimate the quality of idiots that will be running your machines
http://aabeck.com
  Reply With Quote
Old June 13th, 2018, 10:09 AM   #10
jfrye
Member
United States

jfrye is offline
 
Join Date: Oct 2017
Location: Charleston
Posts: 7
I've bypassed the switch and ran comm cable directly between the HMI and PLC, PLC and HMI are both new in case the ports were bad. Currently the setup is PLC to switch and switch to HMI, I do not believe we setup a direct connection since the two units were replaced.
  Reply With Quote
Old June 13th, 2018, 10:10 AM   #11
jfrye
Member
United States

jfrye is offline
 
Join Date: Oct 2017
Location: Charleston
Posts: 7
The HMI was programmed by a vendor, and the original config/program is proprietary.... We can get into the PLC in development mode, but not the HMI.
  Reply With Quote
Old June 13th, 2018, 10:20 AM   #12
geniusintraining
Lifetime Supporting Member + Moderator
United States

geniusintraining is offline
 
geniusintraining's Avatar
 
Join Date: Jun 2005
Location: SC
Posts: 5,559
Quote:
Originally Posted by jfrye View Post
The HMI was programmed by a vendor, and the original config/program is proprietary.... We can get into the PLC in development mode, but not the HMI.
Now that sucks...
__________________
www.PLCCable.com PLC Communication Cables, PLC Trainers, Fluke Meters, MicroLogix, ControlLogix, Siemens, Allen Bradley and more... all your automation needs... ((NEW)) After Market 1784-U2DHP Allen Bradley USB to DH+ and Gateways
  Reply With Quote
Old June 13th, 2018, 10:56 AM   #13
jfrye
Member
United States

jfrye is offline
 
Join Date: Oct 2017
Location: Charleston
Posts: 7
Quote:
Originally Posted by geniusintraining View Post
Now that sucks...
Yes, yes it does. We are planning to sometime in the future recreate the HMI in CMore and abandon the overpriced PVP... but that doesn't help the immediate future.
  Reply With Quote
Old June 13th, 2018, 12:29 PM   #14
jfrye
Member
United States

jfrye is offline
 
Join Date: Oct 2017
Location: Charleston
Posts: 7
Quote:
Originally Posted by rdrast View Post
^^^ This.


This has nothing to do with your rack, it is a communications fault between the PLC CPU and the HMI. That is all it is.


I'm actually surprised that you can even read the output and input images directly, I haven't used an SLC is a long time, but I seem to remember that the I and O image tables can't usually be read by most communications software.
We tested this theory, unplugged the HMI from any connection with the PLC and tested function. The PLC/machine kept in operation the entire time the HMI was disconnected, the timeout alarms did output on the HMI...


We are going to verify that the PID output(s) are not running through the HMI before going to a VFD as a speed input.
  Reply With Quote
Old June 14th, 2018, 12:25 AM   #15
janner_10
Supporting Member
United Kingdom

janner_10 is offline
 
Join Date: Dec 2014
Location: Tewkesbury
Posts: 622
I would download Advanced HMI, add in some tags from the SCL and get it running on a laptop, if Advanced HMI works whilst the original HMI produces errors, you have shown the SLC is good and the HMI is bad.

Move on and add in your own HMI. You have many options for a replacement HMI available to you.
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
Multiple Profinet IO systems? ahuberee LIVE PLC Questions And Answers 1 April 18th, 2018 10:42 AM
Remote IO for Compactlogix DwSoFt LIVE PLC Questions And Answers 11 February 8th, 2018 12:22 PM
WinCC Flex. Set focus on IO field? smcmanus LIVE PLC Questions And Answers 10 February 10th, 2017 06:00 AM
CLogix DHRIO to 1791 Block IO Peter Laing LIVE PLC Questions And Answers 2 August 31st, 2015 11:35 AM
Remote IO nodes using Flex IO or CLX? flyers LIVE PLC Questions And Answers 12 June 15th, 2009 12:01 PM


All times are GMT -5. The time now is 12:44 PM.


.