Increace current consumption in S7 1215C

Hi,

I am programming an S7 1215C to function in a sudo SCADA demo. I am running the 120V supply for the 1215 through a voltage and current transducer. These 2 transducers are in turn feeding the 2 onboard analog inputs. I am trying to determine the easiest way to periodically run logic that would increase the current draw of the 1215C so I can make less static dashboards. Any suggestions would be greatly appreciated.
  Reply With Quote
Old June 13th, 2018, 09:37 AM   #2
cardosocea
Member
United Kingdom

cardosocea is offline
 
Join Date: Nov 2016
Location: Fields of corn
Posts: 1,029
Run a motor? Start a Heater? Both?
  Reply With Quote
Old June 13th, 2018, 09:54 AM   #3
Pete_S
Member
United States

Pete_S is offline
 
Join Date: Mar 2015
Location: Portland Maine
Posts: 69
Quote:
Originally Posted by cardosocea View Post
Run a motor? Start a Heater? Both?
Sorry I should have clarified. I am trying to increase the current consumption of the S7 1215C with logic. So the logic that would put the highest load on the CPU is what I am thinking but not really something they spec in the manual.
  Reply With Quote
Old June 13th, 2018, 10:18 AM   #4
janner_10
Supporting Member
United Kingdom

janner_10 is offline
 
Join Date: Dec 2014
Location: Tewkesbury
Posts: 646
You're better off just using logic within the PLC to simulate an analogue input go higher and lower.

I doubt the current draw of a empty plc and a PLC full of logic will be so negligible, it would almost be immeasurable.

Unless I mis-understand your question.
  Reply With Quote
Old June 13th, 2018, 10:29 AM   #5
Pete_S
Member
United States

Pete_S is offline
 
Join Date: Mar 2015
Location: Portland Maine
Posts: 69
Quote:
Originally Posted by janner_10 View Post
You're better off just using logic within the PLC to simulate an analogue input go higher and lower.

I doubt the current draw of a empty plc and a PLC full of logic will be so negligible, it would almost be immeasurable.

Unless I mis-understand your question.
No, you understand my question. So current draw is not a function of logic processing? I understand it it is probably not a linear relationship, but I would think there would be some increase in current draw. I was thinking simulating large recipe edit by moving a boat load of registers. OB1 with a few networks running random number generator FB's and my signal scaling is a negligible current draw. Guess I would have to load outputs to really see an increase in current? I don't have any peripherals to drive with outputs but I could in theory just run resistors of appropriate value from output to ground, or even from output to input, which would increase the load on the power supply. Thoughts?

Last edited by Pete_S; June 13th, 2018 at 10:35 AM.
  Reply With Quote
Old June 13th, 2018, 10:44 AM   #6
BryanG
Member
United Kingdom

BryanG is offline
 
Join Date: Feb 2005
Location: Manchester
Posts: 1,280
It depends on the sensor you are using to measure current. If it will see very small changes then just switching outputs on and off will increase/decrease the current drawn, more so if they are relay outputs. If it won't see small changes then resistors at a suitable wattage gives you more options and control. Watch out for heat dissipation and having live connections to resistors in places that might get touched.
  Reply With Quote
Old June 13th, 2018, 12:14 PM   #7
Pete_S
Member
United States

Pete_S is offline
 
Join Date: Mar 2015
Location: Portland Maine
Posts: 69
Quote:
Originally Posted by BryanG View Post
It depends on the sensor you are using to measure current. If it will see very small changes then just switching outputs on and off will increase/decrease the current drawn, more so if they are relay outputs. If it won't see small changes then resistors at a suitable wattage gives you more options and control. Watch out for heat dissipation and having live connections to resistors in places that might get touched.
Could I just use the output to drive the corresponding input, Ie Q1=I1? Then increasing current draw in theory as output and input circuits would be consuming power.
  Reply With Quote
Old June 13th, 2018, 12:37 PM   #8
BryanG
Member
United Kingdom

BryanG is offline
 
Join Date: Feb 2005
Location: Manchester
Posts: 1,280
Obviously you must NOT connect 110V to any DC output or inputs, or you will briefly pull a lot of current and let the smoke out.

From the manual a light loaded 1215 with an AC supply will take 100mA, a fully loaded one would take 300mA.

Connecting outs to ins will increase current consumption, but you are talking very low mA.

Inputs take about 5mA each but that is 24V d.c.. So 5mA at 24V is 0.12 watts, 0.12 watts at 110V is 0.0011mA plus inefficiency in the supply. Very low mA change to sense.

Something to be aware of is that there will be up to a 20Amp inrush as you power up the PLC, make sure your sensor can cope with that.
  Reply With Quote
Old June 13th, 2018, 02:03 PM   #9
mk42
Member
United States

mk42 is offline
 
Join Date: Jun 2013
Location: MI
Posts: 1,914
Quote:
Originally Posted by Pete_S View Post
No, you understand my question. So current draw is not a function of logic processing? I understand it it is probably not a linear relationship, but I would think there would be some increase in current draw. I was thinking simulating large recipe edit by moving a boat load of registers. OB1 with a few networks running random number generator FB's and my signal scaling is a negligible current draw.
Realistically, the PLC is always running the CPU at full blast all the time, and the code you run doesn't change how hard it is working. It's hypothetically possible that there might be some minuscule difference in power draw between different operations, but I doubt it would be meaningful. These aren't like an i7 that have technology built in to run slower at lower demand. Every PLC I've ever worked with was single threaded, at least for the main logic.

Slightly related, I read an interesting paper last fall about someone who was pointing a big antenna at a 1200, and could detect some frequency differences, based on copying a big or small DB.

Realistically, it's like the other posters have said. You're going to need some real load (even if it is just a resistor or a pot) that you can turn off and on to change the detected values. Or you can just fake it in code, which is what i've seen in almost every demo system ever.
  Reply With Quote
Old June 13th, 2018, 11:29 PM   #10
Rob...
Supporting Member
United Kingdom

Rob... is online now
 
Join Date: Jul 2016
Location: Manchester
Posts: 124
Easier to simulate it.

The AI inputs will not have the resolution needed to make any decent measurements.

Increasing the workload of the PLC will not make it work any harder. Just increase the scan time.
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
s7 1200 & cpu 1215C doesnt work nwzt LIVE PLC Questions And Answers 11 October 4th, 2016 05:02 AM
Powerflex 70 Terrep LIVE PLC Questions And Answers 14 March 31st, 2015 09:07 AM
On the subject of inrush current Steve Bailey LIVE PLC Questions And Answers 24 September 1st, 2003 06:19 PM
how to get the current date and time from s7 300 cpu? notfish LIVE PLC Questions And Answers 3 May 31st, 2003 02:17 PM
Monitoring motor current Tim LIVE PLC Questions And Answers 51 April 9th, 2003 06:53 PM


All times are GMT -5. The time now is 11:15 AM.


.