Mitsubishi A1SJH to Indusoft

edpg1

Member
Join Date
Nov 2012
Location
Ontario
Posts
19
Hi Guys,

Hoping someone here can help me.

We have a customer that is using the Mitsubishi A1SJH PLCs, they have a few of these throughout their plant. They are working fine, it's the HMIs that are starting to fail, and are becoming harder and more expensive to replace/repair them.

We are trying to find an alternate solution to these HMIs and use Indusoft for our Beckhoff projects, and we know it has a multitude of drivers, it even has 3 different Mitsubishi drivers.

When I use the Mitsubishi-A driver (Apparently the proper driver), I get an Error stating "Timeout Waiting to Start a Message". According to Indusoft documentation it's one of the following issues:

Cables (The GX Developer Software connects to the PLC no problem, using official SC-09 cables)
PLC is off or not in Run (I'm not that dumb)
Wrong Station Number (no Documentation, tried every number up to 31)
Wrong RTS/CTS control settings (I've tried all four options, No,Yes,Yes+Echo,Always On)

I've contacted Indusoft support, who seems perplexed by this, they are trying to find the device they got their driver certified on. Mitsubishi is being no help because it's not a Mitsubishi problem.

The only thing Mitsubishi support provided me was the correct settings: 9600baud, 8 bits, 1 stop, odd parity.

Has anyone been successful between one of these Mitsubishi and Indusoft? Anyone have any suggestions?

Thanks,
 

Similar Topics

Hi all, Im a beginner a programming PLC's, so if anyone help with some of my questions, that would be highly appreciated. Currently I'm working...
Replies
5
Views
3,560
Hello all, I am using MEDOC software package Version 1.64C and I have new PLC with CPU type A1SJH. This type of CPU is not mentioned in the PLC...
Replies
3
Views
5,978
Hi Everybody Can anybody tell me what is the difference between R(File Registers) and D(Data Registers) even i go through the programming...
Replies
3
Views
6,500
Unregistered
U
I'm looking to get some spare keys for this PLC. Does anyone know a source or have a part number? My searches are turning up nothing at the moment.
Replies
1
Views
64
I'm struggling to get an FR-E800SCE to work on CC-Link IE TSN. I'm sure the issue is with the drive, when I plug in the network cable I get no...
Replies
1
Views
90
Back
Top Bottom