Got another one a whole team of us and the OEM cannot figure out.
Powerflex525, 20HP VFD, commanded over Ethernet won't turn a motor it's turned its whole life all of the sudden. Drive doesn't fault. Replaced the drive with a used one (love supply chain) same results.
Verified all wiring and motor megs okay. Wire motor directly to MCB and it starts and runs fine. Pulls even 10 amps on all legs with empty auger. 20HP motor, 27 amp FLA.
According to drive parameters while running:
Command Frequency = 60hz
Output Frequency = 60Hz
Output Voltage = 456vac
Output current = .27amps
Motor Nameplate FLA =27
Motor OL = 30
No safety wired to drive, STO jumper is still in place. Only Enable signal is wired in and verified voltage is present there.
When trying to run the motor from the drive with it in the above state, input voltage is steady 480ish across all three phases. Actual measured voltage out of the drive is 35ish VAC. We have not amp clamped the wires when running motor from the drive.
Given the same results on both drives it feels like a parameter issue but none of us can figure out what we're missing. Thoughts on what else to check?
Powerflex525, 20HP VFD, commanded over Ethernet won't turn a motor it's turned its whole life all of the sudden. Drive doesn't fault. Replaced the drive with a used one (love supply chain) same results.
Verified all wiring and motor megs okay. Wire motor directly to MCB and it starts and runs fine. Pulls even 10 amps on all legs with empty auger. 20HP motor, 27 amp FLA.
According to drive parameters while running:
Command Frequency = 60hz
Output Frequency = 60Hz
Output Voltage = 456vac
Output current = .27amps
Motor Nameplate FLA =27
Motor OL = 30
No safety wired to drive, STO jumper is still in place. Only Enable signal is wired in and verified voltage is present there.
When trying to run the motor from the drive with it in the above state, input voltage is steady 480ish across all three phases. Actual measured voltage out of the drive is 35ish VAC. We have not amp clamped the wires when running motor from the drive.
Given the same results on both drives it feels like a parameter issue but none of us can figure out what we're missing. Thoughts on what else to check?