I have an IP camera, Amcrest IP8M-2493E, that has some digital I/O capability. It has 3 wires:
Alarm_IN1
Alarm_OUT1
Alarm_GND

I would like to integrate this I/O to a PLC. If I short the IN1 and GND, via relay contacts from my PLC, I get a signal to the camera and it does what I intend.

However, I can't figure out how to tie the camera output to a PLC input.

The camera Alarm interface is described in the manual as "1 channel In: 5mA 5VDC 1 channel Out: 300mA 12VDC". This seems to conflict with a sketch shown in a video (https://youtu.be/I7pGznSbsBs at the 1:51 mark) that shows +3.3V power and a 5V/5mA max. output capacity.

I've tried the 10k resistor in a pull up configuration with both 12VDC and 5VDC power. Should I be using a 3.3 volt power supply? With either 12VDC or 5VDC power, I get 12VDC or 5VDC between OUT1 and GND when the output is what I would call "OFF" and 0VDC when the output is what I would call "ON".

Great, the output voltage seems to be working. However when I attach either a 12VDC or 5VDC relay to the output, the relay does not change state and the voltage drops to some low amount.

Amcrest support is almost non-existent. What am I doing wrong? How do I interface this camera output to a signal level that I can do something with?

TIA.
 
Last edited:
Looks like the video and documentation are contradictory.

I think the video is correct and it is a sinking output which matches your operation description.

I get 12VDC or 5VDC between OUT1 and GND when the output is what I would call "OFF" and 0VDC when the output is what I would call "ON".

The output will be 0VDC when on.
The output will be the supplied VDC when off.
The logic is reversed for this type of output.

You could use the output to switch an interposing optocoupler relay, which then drives the plc input.

If the plc input switches states at 12VDC you may be able to wire it directly to the input without the relay.

Capture.png
 
I got a 5VDC solid state relay very much like the Phoenix Contact part mentioned, wired it up per the diagram above and seems to work perfectly.

Thanks for the info.!
 
I got a 5VDC solid state relay very much like the Phoenix Contact part mentioned, wired it up per the diagram above and seems to work perfectly.

Thanks for the info.!


just make sure that the input current draw of the relay is below the 5ma max of the camera
 
It pulls about 3 mA for a brief instant which I guess would be the inrush and then goes to a very low current after that. Thanks.
 

Similar Topics

Hello all I've got a cell with four Keyence IV3 cameras that are saving images to a FTP server, we are also labeling the parts with a time date...
Replies
3
Views
238
The data structure I'm looking for for the inputs and outputs from the camera is Dint[125]. When I installed the CV-x300 Keyence module it is...
Replies
2
Views
331
I have a Cognex Insight 2000-130 camera that I'm trying to get talking to my PLC. Both are connected to the same router via Ethernet. Thus far...
Replies
12
Views
1,207
Hello, i am a uni student and i am trying to specialize in automation, i always had this project in mind that i can sort different items, for...
Replies
7
Views
913
Hello All, We have a customer where we are trying to help diagnose and fix hydraulic leaks. Because of the operator of the machines, we cannot be...
Replies
13
Views
4,420
Back
Top Bottom