Hi,

I got a question about electrical shielding.
For profibus in the past, shielding was a must and important.

I still remember that we did the following standard shieldment methods:
- Analogue signal cables: 1 side shielding (antenna)
- Frequency converter motor cable: 2 side shielding
- Profibus: shield on every cable that enters the closet.

What about profinet...
Some integrators still do shielding on the backplate in closet like profibus cables, but some don't. Is it a must... what are the basic rules about profinet cabling ?

Thanks,
Kind regards,
Combo
 
I personally prefer to shield any cable that carries data or signal. The additional cost of shielded cables is usually less than even one time of hunting down an intermittent fault that is being caused by noise. It can be difficult to isolate and even worse to rip-out non shielded cables and replace with shielded after the fact.

Especially when the noise causes degraded system performance and not a true fault, the money that can be lost in product quality and/or cycle time can be a hidden cost that typically grows with time.
 
Can you get by without it? Usually, except when you can't.

dlweber is right, just get them. They pay for themselves once you consider troubleshooting.
 
Originally posted by mk42:

Can you get by without it? Usually, except when you can't.

Very well said. I think it's important to acknowledge that it can, and often will, work without shielded cables while also stating that it is a problem waiting to happen, and a very difficult one to diagnose at that. There are just too many working unshielded applications out there today to emphatically state it will never work.

Keith
 
Very well said. I think it's important to acknowledge that it can, and often will, work without shielded cables while also stating that it is a problem waiting to happen, and a very difficult one to diagnose at that. There are just too many working unshielded applications out there today to emphatically state it will never work.

Keith

Interestingly, the newer Ethernet standards for cables are doing away with unshielded cables as an option, but these are only needed for crazy fast speeds Apparently 40gig is coming over copper in the future (Cat 8 cables)
 
We custom fit our cable lengths to the devices on the equipment. Yes...industrial grade Ethernet cable, 2 pair shielded...... but I have been changing to 4 pair for full support of Profinet Gigabit communications.

Inside the cabinet, for short runs to switch, I just use shielded CAT5e (or better) industrial rated patch cables from Automation Direct or...
https://www.automationdirect.com/ad...t.)/cat5e_patch_cables_(shielded_twisted_pair)

Once again..... maintaining 4 pair wiring to support Profinet gigabit devices.
yes...it is shielded....but not necessarily independent pairs shielded., however we are talking less than a 3 ft run in cabinet to switch.
 
Last edited:
As Profinet works over the regular Ethernet media, whatever works for Ethernet, should work for Profinet as well.

However, using shielded network cables is a better option for industrial environments where, unlike office, sources of strong electrical noise can exist.
 

Similar Topics

Does 0-10V signal really need to be shielded if run with 24VDC wiring? How about 120V AC? Does it rally need to be twisted pair shielded? I am...
Replies
19
Views
8,722
Team, I've got an older piece of equipment that is using serial and usb connections. We have started to get garbage data, and I am starting to...
Replies
5
Views
2,549
Hi group, I have (2) 6-foot lengths of cable, one is the HMI serial comm cable between a PLC and an Automation Direct EA9 HMI ....the other...
Replies
13
Views
3,072
Hello, Does anybody know if there is a normative or good practice guidelines for calculation wire cross section of cables used for safety...
Replies
3
Views
1,740
Hello to all, i'm reading the manual regarding this module from Siemens, and since English is not my native language I'm not sure if I understand...
Replies
6
Views
3,688
Back
Top Bottom