PLC/Robot Handshake in Pallet Pro

kuckphoto

Member
Join Date
Nov 2018
Location
Kentucky
Posts
5
I'm having some difficulty with the Handshake between the PLC and the Fanuc Palletizing Robot (M410ic/185 with a R30iB Plus). DO32 turns on and when I turn on DI32 then DO32 immediately turn off without passing the GI data to the robot. I'm sure there's a setting or something I am missing but I'm having difficulty finding it. Has anyone had this issue? Comms between the robot and CompactLogix are via EthernetIP.
 
I'm having some difficulty with the Handshake between the PLC and the Fanuc Palletizing Robot (M410ic/185 with a R30iB Plus). DO32 turns on and when I turn on DI32 then DO32 immediately turn off without passing the GI data to the robot. I'm sure there's a setting or something I am missing but I'm having difficulty finding it. Has anyone had this issue? Comms between the robot and CompactLogix are via EthernetIP.

It sounds like these are signals just being passed through if I understand right.

There's many places this could be.

It could be BG_Logic...You get to it by menu, setup, next, bglogic

It could be PMC editor also in the setup

There's a few more places in the setup where you can tie these together. Also it could be a monitor in the main program.
 

Similar Topics

Hi all, First time posting here. I have a Omron NX1P2-1040DT controller that I intend to use for a small project. I also have a KUKA robot that...
Replies
3
Views
1,178
Hello everyone, For my new project I want to integrate a Staübli Robot with AB PLC. I don't know how to get started with it. How can I integrate...
Replies
3
Views
2,129
I am a college student in my 2nd year of Automated systems and for my final project me and my classmate are looking to hook up a Universal Robots...
Replies
13
Views
5,394
Hi! I'm new to Mitsubishi robots so please bear with me. I have a setup of an RV-7F-Q1-S15 robot with a CR750-07VQ1-1-S15 controller and a PLC...
Replies
1
Views
3,340
On all of our lines that have Fanuc robots, we have the cabinet e-stop and pendant e-stop mapped to seperate DOs for messages purposes. We also...
Replies
5
Views
2,484
Back
Top Bottom