configure 1769 IF4 input module in RS Logix 5000

DannyBoi

Member
Join Date
Aug 2016
Location
St. Louis
Posts
2
I have installed 1769 IF4 analog input module in compact logix rack slot 3. I have an existing 1769 8 channel input card in slot 2 already working. When I go to RS Who I can see the module I just installed, but I cannot figure out how to configure the module. Any help would be appreciated.
 
in RSLogix5000, you need to Right-Click on the Local Bus and ADD the new module to the I/O Configuration list ... (you'll probably need to be OFFLINE to do this) ...

once that step has been done, you should be able to Right-Click on the new module (again - in RSLogix5000) and do the configuration steps ...

basic idea: just because you've physically installed (plugged in the module) it doesn't automatically get added to the I/O Configuration list ...
 
Thank you Ron. This is my first question on this site and am amazed that I was answered so quickly. Just joined yesterday. Many thanks again Ron!
 

Similar Topics

I am trying to add an input to a 1769-IF8 which is being read by a CompactLogix L35E. I want to add a 4 to 20 ma signal into input 3 and have...
Replies
3
Views
2,022
Hi All I've read the manual...didnt understand much... I have a accurate flow meter that gives pulses with certain width. just have to obtain...
Replies
6
Views
2,968
hi all i am new here i have a mitsubishi smart touch hmi i.e ms-60t-pe but i cannot find a software to edit and download a program in it any help...
Replies
3
Views
98
Hello, I am trying to connect a Stride Analog Output module to a 1769 CompactLogix via Ethernet. I added a new Generic Ethernet Module for the...
Replies
4
Views
180
Dear all, I am beginer in ifix hmi programming. I have 2 ifix 6.0 pc with license FiX and client.. Can some one tell me how to configure sample...
Replies
0
Views
114
Back
Top Bottom