Can we transfer PanelView Plus 1500 configuration to PanelView Plus 1250?
wendaiyu
Jun 2014
toronto
87
Hi, guys, how’s going?
Because our PanelView Plus 1500 is defective, but there is only PanelView Plus 1250 in the stock.
Thanks a lot.
The short answer is yes. I'll leave the long answer to someone that knows more about it than I do.
Will.
The PanelView Plus 1250 and 1500 models share the same resolution screen and the same logic module, so if there are no other differences between the terminals the Runtime file should behave exactly the same.
Not quite Ken...
26040 - PanelView Plus and VersaView CE screen resolution
Access Level: TechConnect
De-TechConnected...
PVP 400 = 320x240
PVP 600 = 320x240
PVP 700 = 640x480
PVP 1000 = 640x480
PVP 1250 = 800x600
PVP 1500 = 1024x768
From the above you will notice that the PVP 1250 has a resolution of 800x600 and the PVP 1500 has a resolution of 1024x768. If you change "Project window size" in an application, to one of a different resolution, then you will be prompted that scaling of the displays must be performed during conversion.
But yes, it is all quite possible. The level and complexity of the application's graphics and/or images used will determine how successful the conversion will be. If the graphics or images end up distorted looking then you cannot revert. That is why they advise you to backup your application before attempting to change the application's window size.
So just back it up and then try change to a PVP 1250. You might have to mess around with some of those scaling options to get it right. But then again, you might not?
Regards,
George
Newbie so sorry if this question is very general or has been discussed elsewhere already. We have a R/O system installed presently and I am...
2,548
PanelView Plus 7 1500 F/W v9 What would cause one person be able to see the PV in the transfer utility but not another? I have a guy on site...
15,111
Hi, guys, how’s going? How to transfer applications from Panelview Plus to PC, then configure it via Factorytalk View ME? There are 4...
2,037
Hello everyone. I posted about a week ago for advice on breaking into an older PV+ to get to the desktop. (HERE) I found that I really can't get...
20
27,317
I cannot pull the .mer off the panelview the transfer fails saying i do not have a valid source (mer). This panel view does not have a config...
2,447