to me, the big issue is all the area classifications. while you can get an hmi for zone 2, adding the IIa,IIb, T3 onto that means that not only do you have to design for those areas, you must now investigate the following:
zone 2 chemical deposits onto the hmi, along with IIa,IIB, T3 chemical deposits, and MOST importantly, chemical interaction with each other and reactivity with the hmi components.
from personal experience, it is no fun. you need to have your i's dotted and t's crossed, specify to the customer what he is getting and the chemicals that can and cannot be used.
james
 
I'm not sure what you're on about James...

T3 is the temperature level under which equipment can be installed in that area. So T4, 5 and 6 will do.

IIB is the gas group that the equipment must meet. In this case, IIB or IIC will do.
Zone, gas group and temperature (bearing in mind ambient temperature) need to be met for the equipment to safely be installed in a certain area.



If there are chemicals being deposited in the equipment (in this case, the HMI) it's a zone 0 and no HMI in the market can be installed in there. But maybe I misunderstood.
 
cardosocea,

thanks for pointing out that t3 is temperature.
in my last post, i was simply trying to alert the designer what to look out for based on previous experience. it's easier to find the problem before the machine gets built and installed rather than having the customers safety team tell you that their research found that the hmi cannot be used. Trust me on this point ! i failed multiple machines due to hmi panels not meeting our requirements that were in the quotation spec sheet. the OEM was not a happy camper, but he had to replace them at his cost.
james
 

Similar Topics

Hi, I have a Class 1 Div 2 HMI and would like to supply the 24 Vdc power through an isolation barrier. I cannot seem to find any barriers out...
Replies
19
Views
4,057
Hello All, We have a HMI ,a Mecury 2e Intrinsically Safe HMI. Does anyone know what is required to 1: Download an existing backup to a HMI or 2...
Replies
0
Views
2,633
It is my understanding that an LED is considered a simple device, making its use fairly simple in an IS application. However I am running into a...
Replies
22
Views
5,810
Hey, does anyone have any experience with such a device? I need to have an RFID reader set up in one of the paint booths we have. Thanks! -PreLC
Replies
3
Views
1,518
I had a chat today with a contractor and he notified me that Rockwell will stop producing the Flex Ex IO modules from December 31st. The ones we...
Replies
4
Views
1,641
Back
Top Bottom