FT View SE 9 not reading output card

LSPort

Member
Join Date
Dec 2016
Location
uk
Posts
29
I am building a new SE display for a pre-existing machine in my facility.
The target controller is SLC5/05 , this controller uses slot 23 output card to drive pneumatic solenoids on the machine and they are operating correctly.

However when i have configured the animation on the SE Display wherever this one particular card bits are used the animation errors with the blue err displayed.

I have set up test animations on the display triggered by all other cards and they work fine.

The output card is a standard OB16 as are most of other o/p cards in this rack
I have copy and pasted existing working tag connections and amended slot number to suspect slot and they still do not work.

I worked around the issue by copying the suspect word to a B3 Word, then retagging the animation properties in SE and all works.

Has anyone come across similar before ?

Thanks for your time.
 

Similar Topics

Hi guys! I want to read a tag name of hmi tag to create a generic alarm message. Do you know if it's possible to do? I'm using factorytalk view...
Replies
1
Views
707
Hello all. I am working with a CompactLogix running version 30.12, and a Panelview Plus 700 running version 9.0. The customer wants me to read...
Replies
8
Views
4,106
Hi everyone, I have been tasked with the job of setting up FT View SE SCADA for a compact logix PLC. There are also a few points that need read by...
Replies
4
Views
2,629
I am fairly new to Controllogix and have been thrown into the deep end in a Project. I am trying to read my digital input tags from the plc...
Replies
3
Views
6,287
PanelView Plus "Timeout Reading" and "Timeout Writing" - battery low Hi all, A customer has a PanelView Plus (catalog number 2711P-K4M20D8 ser...
Replies
5
Views
4,381
Back
Top Bottom