I am trying to communicate with an Acromag 951EN-6112.
I have a Compactlogix 1769-L36ERM
I have loaded the EDS file for the acromag
I have configured the module.


The acromag is in another building however,

I can ping the module.
I can get to the module's webpage from within my PLC network.
I can see the module in RSLIX Classic.


I am getting a (Code 16#0203)Connection Timeout Error followed by a Code 16#0113) Connection Request Error: Module Connection Limit Exceeded.


This is the only Ethernet connection on the PLC.



Any ideas??


thanks in advance
 
fixed the newel post

So the issue is that the default Data config is DINT. The data is INT.


I had to delete the module and rebuild it but it works now.


Thx
 
Thanks very much for that followup !

I would have expected a different error code for a size mismatch; the data type shouldn't matter on a Generic Ethernet Module connection.

But I'm glad you got it working !
 

Similar Topics

I am looking at this combo for a project where the client has specified the AB 1400 but also has 9 RTDs to monitor. As the RTDs would consume 3...
Replies
0
Views
1,626
I have four used 983EN-4012 I/O Modules. I have followed the "reset to default" proceedure very carefully numerous times and still cannot connect...
Replies
0
Views
1,866
I received an email from a student with the following code attached. This is supposed to control a floodgate system, and supposed to be written...
Replies
18
Views
360
I have a machine which is undergoing upgradation. As part of the process two SEW drives are being replaced., existing Gen B with new Gen C. The...
Replies
3
Views
168
I want to set user security level based on the value of a tag in my PLC called "ActiveUser". That tag will contain the A-P code which we use for...
Replies
6
Views
202
Back
Top Bottom