I have a few questions regarding the UL508A specification.
I believe this spec. requires a seperation of power and control wiring/devices in a control panel. What is required to comply with the term "seperation"? The system I am talking about is 208V 3ph. power and 120V control. It is a small panel: 2 motor starters, Micrologix 1000, disconnect etc.
__________________
SSC Automation Last edited by 93lt1; September 2nd, 2004 at 10:13 AM. |
|
|
|
#2 |
|
Member
|
For starters you are not allowed to run power wiring and control wiring in the same busway(Panduit) or bundled together.
I always had at least an inch of seperation where wires had to run parallel and never had a problem with my UL inspector. In my dealings with UL using common sense was typically the right thing to do. Your mileage may vary... |
|
|
|
#3 |
|
Member
|
Is there any other little know facts, oddball stuff, etc.?
__________________
SSC Automation |
|
|
|
#4 |
|
Member
|
The stipulation is that they must be physically separated. The spec also states that in a wireway there must be some physical device or construction practice that can accomplish this separation. In practice we usually use panduit like 2 2inch panduit (one is stripped of one side) and place them under a 4inch cover. Other physical means are acceptable, for one OEM we separate the Medium Voltage (high voltage doesn't start until greater than 600 volts?)with a grounding mesh of copper braid that is anchored by the panduit mounting screws every 4 inches. But as was started before "results may vary!" Crossing wires has never been an issue with any inspector I know, as long as, the insulation of both conductors is rated for the highest voltage present.
just a bitmore
__________________
"A good scientist is a person with original ideas. A good engineer is a person who makes a design that works with as few original ideas as possible. There are no prima donnas in engineering." Freeman Dyson Last edited by Bitmore; September 8th, 2004 at 12:27 AM. |
|
![]() |
| Bookmarks |
| Currently Active Users Viewing This Thread: 1 (0 members and 1 guests) | |
| Thread Tools | |
| Display Modes | |
|
|
Similar Topics
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| UL 508A Class | ndzied1 | LIVE PLC Questions And Answers | 8 | July 12th, 2004 09:13 AM |
| UL Listed panel shop | RDay | LIVE PLC Questions And Answers | 5 | January 11th, 2004 06:59 PM |
| "E-Terminals" opinions... | Eric Nelson | LIVE PLC Questions And Answers | 41 | January 6th, 2004 02:39 AM |
| 230v Estop | Steve Crotty | LIVE PLC Questions And Answers | 30 | March 17th, 2003 07:46 AM |
| UL Ratings | MCMOORE41 | LIVE PLC Questions And Answers | 7 | January 29th, 2003 02:53 PM |