plc storereviewsdownloads
PLC training tools sale
Reply
Thread Tools Display Modes
Old September 6th, 2004, 08:56 PM   #1
Doug_Adam
Australia
Doug_Adam is offline
Doug_Adam's Avatar
OT Wire Colours for Aussies and Kiwis (Others welcome to join in)
Just trying to see if there is any common practice for wire colours for 24V DC wires around the antipodean countries.
So far I have encountered the following colour schemes:
24V DC ----------0V DC
Grey/Red Stripe --- Grey
Violet ----------- Grey
Orange ------------ Grey
Orange ------------- Blue
Grey ---------- Light Blue
This has been for internal panel wiring.
All of these appear to be allowed in the A/NZ Standards.
I would like to know, what have you encountered?
What do you prefer?
My personal preference was the Grey/Red stripe and Grey scheme, but it suffered from Grey/Red stripe not always being available.
I don't really want to exclude non Australians/New Zealanders from this thread, but it is more of a local knowledge question.
Doug
Old September 7th, 2004, 02:12 AM   #2
westoes
Australia
westoes is offline
westoes's Avatar
Lightbulb
Doug our Australian company exports MCC's OS and it was the standard for Europe for 24vdc + and 0vdc to be both purple/violet.But roughly 3 years ago we were informed that the new standard is "dark blue" for both 24v+ and 0v,and believe it or not "light blue" for 220vac neutral.
This is not set in concrete as you will always come across customers with different specifications.
banghead banghead
Old September 7th, 2004, 02:28 AM   #3
Doug_Adam
Australia
Doug_Adam's Avatar
So you are saying that the 24V DC positive and common are both the same colour?
Old September 7th, 2004, 02:31 AM   #4
Doug_Adam
Australia
Doug_Adam's Avatar
The light blue for 220V Neutral I can understand, since I think our common practice of Brown/Light blue for flexible cable seemed to come out of Europe.
Old September 7th, 2004, 05:09 AM   #5
thierry2003
Belgium
thierry2003 is offline
thierry2003's Avatar
Where I work we use grey for +24V, purple for 0V, in between is blue.
I don't know if that is the standard but all panels are done by a proffesional company so I suppose they'll know the standards.
Old September 7th, 2004, 07:04 AM   #6
rsdoran
United States
rsdoran is offline
rsdoran's Avatar
IEC 204-1 should give you the European standard. I dont have it just excerpts pertaining to green/yellow for grounding and light blue for the neutral conductor.
In the US the quideline is determined by NFPA 79 16.1.2
GREEN with or without yellow stripe: Ground
BLACK: Line, load, and control at line voltage
RED: Control conductors at less than line voltage
BLUE: ungrounded DC control conductors
Yellow: ungrounded control conductors that may remain energized when the main disconnect is OFF.
Orange is used by IEC 204-1 for this purpose
White or Natural Gray: Grounded circuit conductor
White with Blue stripe: Grounded DC (current carrying) conductors
Light BLUE is IEC 204-1 neutral conductor
White with yellow stripe: Grounded ac conductor that may remain energized when main disconnect is OFF.
Someone once asked about using splices in a panel
16.1.4 Conductors and cables shall be run without splices from terminal to terminal
Excption: Splices shall be permitted to leads attached to electrical equipment, such as motors and solenoids, such spices shall be insulated wuth oil-resistant electrical tape or insulation equivalent to that of the conductors.
__________________
http://www.patchn.com Industrial Electrical & Maintenance @ www.patchn.com "Tell me and I forget, show me and I remember, involve me and I understand."
Old September 7th, 2004, 03:57 PM   #7
westoes
Australia
westoes is offline
westoes's Avatar
Yes doug both + and ov are the same colour but as you can see from the posts so far it doesn't seem that there is a stringent voltage/colour standard.At the moment our colour code we wire to is :380-440vac 3 ph all black 220vac active-brown neutral-light blue 24vdc +&ov-dark blue.For VSD shielded cable the combination is brown-blue-black.
In saying this there have been occasions where we have used all of the above colour codes because that is the standard they have in use and prefer to keep it all the same.
banghead banghead
Reply
Bookmarks
Thread Tools
Display Modes
Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts
BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump
