Logix 5000 First Scan Bit
I know that to get the first scan bit out of a CL5000 processor, you need to use a GSV. But that is as far as I get. I cannot find the actual first scan object. Can anyone tell me where to get this, or post a screen shot of a GSV in which they got this bit? Thanks.
Russ |
|
|
|
#2 |
|
Member
![]() Join Date: Jun 2002
Location: Auckland
Posts: 1,134
|
Use a XIO or XIC instruction with address S:FS
No GSV required. |
|
|
|
#3 |
|
Member
|
Gerry is right. Browse the on-line help for "Monitoring Status Flags". You'll find several S: flags, such as S:C for carry, S:N for negative result and S:MINOR for detection of minor faults, besides S:FS for first scan.
Kind regards,
__________________
Jean Pierre Vandecandelaere Trainer nautical sector VDAB Competentiecentrum L. Blondeellaan 9 B-8380 Zeebrugge Belgium |
|
|
|
#4 |
|
Member
|
Thanks guys! I was wondering about that, too!
Especially since the "power-up" routine is exactly that. Don't expect the power-up tasks to get executed unless you unplug the controller. Switching from Program to Run doesn't do it. AK |
|
![]() |
| Bookmarks |
| Currently Active Users Viewing This Thread: 1 (0 members and 1 guests) | |
| Thread Tools | |
| Display Modes | |
|
|
Similar Topics
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| RS Logix 5000 instruction | stantana | LIVE PLC Questions And Answers | 5 | April 9th, 2008 08:25 AM |
| 10 Bit Encoder Decoder/ GE90-30 | Control Freak | LIVE PLC Questions And Answers | 6 | July 12th, 2005 11:28 AM |
| Update/evaluation of internal relays/contacts...PLEASE HELP | s_viswesh | LIVE PLC Questions And Answers | 18 | October 14th, 2002 01:58 PM |