Digital offset on analog input

On a Micrologix 1100 analog input, I appear to be getting an internal offset of about 11 counts out of 1023.
Running the program from RSLogix, when I look at N7:35, which is only written by the analog input, I see 6 counts out of 1023 when the analog input is shorted at the PLC input. If there is no applied input (and the short removed) I see 11 out of 1023 counts.
The measured input voltage in this case is .001 volts.

Does someone know where this offset comes from? It appears to be completely internal to the PLC.
  Reply With Quote
Old December 22nd, 2016, 02:56 PM   #2
g.mccormick
Member
United States

g.mccormick is offline
 
Join Date: Jul 2012
Location: IN
Posts: 465
Just offset/inaccuracy of the A/D in the card I'd assume.
  Reply With Quote
Old December 22nd, 2016, 02:58 PM   #3
wildcatherder
Member
United States

wildcatherder is offline
 
Join Date: May 2009
Location: Morro Bay
Posts: 168
Out of cal?

You would certainly think zero would be factory-calibrated.
  Reply With Quote
Old December 22nd, 2016, 03:02 PM   #4
g.mccormick
Member
United States

g.mccormick is offline
 
Join Date: Jul 2012
Location: IN
Posts: 465
What is the stated accuracy?
6/1023 * 100 = 0.5% of zero reading.

Is it really 1023, so 10 bit?
  Reply With Quote
Old December 22nd, 2016, 03:08 PM   #5
wildcatherder
Member
United States

wildcatherder is offline
 
Join Date: May 2009
Location: Morro Bay
Posts: 168
10-bits input

Overall accuracy is shown as +/- 1% full-scale, so that is 10 out 1023 and is good as it gets.

We were using the Micrologix 1000 with 16-bit input but switched because the 1000 is being discontinued.

Well, that's another mystery solved.

Thank you, G. McCormick for your assistance in this matter.

Last edited by wildcatherder; December 22nd, 2016 at 03:20 PM. Reason: added thanks
  Reply With Quote
Old December 22nd, 2016, 03:36 PM   #6
g.mccormick
Member
United States

g.mccormick is offline
 
Join Date: Jul 2012
Location: IN
Posts: 465
happy to help.

It's rare that I actually can help someone on here
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
RTD vs Current analog input devices . (beckhoff to be exact ) awaisq LIVE PLC Questions And Answers 12 July 1st, 2015 08:31 AM
Point IO rack size the_msp LIVE PLC Questions And Answers 8 December 11th, 2014 11:26 AM
Analog input / Analog Output - Twin CAT System tech007 LIVE PLC Questions And Answers 1 September 30th, 2011 05:21 PM
analog as a digital input MLX1100 nzfy LIVE PLC Questions And Answers 4 March 22nd, 2011 08:40 AM
ML1100 analog input help kbradray LIVE PLC Questions And Answers 6 December 11th, 2007 05:13 PM


All times are GMT -5. The time now is 12:22 AM.


.