plc storereviewsdownloads
PLC training tools sale
Reply
Thread Tools Display Modes
Old March 27th, 2017, 12:27 PM   #1
jrsnydley
United States
jrsnydley is offline
Tag Editor Scaling in Connected Components Workbench
I have a 2711R-T4T that I am hooking up to a MicroLogix 1400 to replace a PanelView Micro 300. There is a tag I am trying to configure in Connected Components Workbench for the HMI. In the old PanelView, the tag is configured as follows:
Tag Name: Yield
Data Type: Signed Integer/Int
Address: N17:110
Scale: 0.001
Min: 0
Max: 32
In the tag editor for CCW, the tag is configured as follows:
Tag Name: Yield
Data Type: 16 Bit Integer
Address: N17:110
Data Entry Min: 0
Data Entry Max: 32
Scaling: ✓
Raw Min: 0
Raw Max: 32
Scaled Min: 0
Scaled Max: 32000
It appears that the numeric entry works correctly but I have the same tag (Yield) used as the Indicator Tag and the value that is displayed is not the same as what is displayed on the original PanelView. It appears to be rounding the value up to the nearest whole number. I have the Numeric Entry formatted as follows:
Decimal Point: Fixed Position
Group Separator: Use Language Preference
Keypad Type: Numeric
Maximum Value: 999
Minimum Value: 0
Negative Number Formats: In Front
Number of Decimal Places: 3
Numeric Field Width: 5
Is there a way I can get this indicator to read as it did on the old PanelView? For example, read 1.234 instead of 1?
Old March 27th, 2017, 02:01 PM   #2
gclshortt
Canada
gclshortt is offline
gclshortt's Avatar
"In the tag editor for CCW, the tag is configured as follows:
Tag Name: Yield
Address: N17:110 "
You have a data type of Integer. Try a Real data type.
This may help you out.
Regards,
__________________
Garry
https://www.accautomation.ca
Connect with us on Facebook: facebook.com/accautomation/
Old March 27th, 2017, 02:14 PM   #3
jrsnydley
United States
Thank you for the response! However, that approach did not seem to help. It gives me a warning saying there is an inconsistency with the data type which I ignored, but the indicator tags still do not read any decimal places.
Old March 27th, 2017, 03:07 PM   #4
gclshortt
Canada
gclshortt's Avatar
What about a DINT or INT signed integer?
The tag must be addressed the same way at each end.
CCW supports the 19 elementary IEC 61131-3 data types below.
• BOOL: Boolean, True or False
• SINT: 8-bit signed integer, range -128 to +127
• USINT: 8-bit unsigned integer, range 0 to 255
• BYTE: 8-bit unsigned integer, range 0 to 255
• INT: 16-bit signed integers, range -32768 to 32767
• UINT: 16-bit unsigned integers, range 0 to 65535
• WORD: 16-bit unsigned integers, range 0 to 65535
• DINT: 32-bit signed integers, range -2147483648 to +2147483647
• UDINT: 32-bit signed integers, range 0 to 4294967295
• DWORD: 32-bit signed integers, range 0 to 4294967295
• LINT: 64-bit signed integers, range -9223372036854775808 to 9223372036854775807
• ULINT: 64-bit unsigned integers, range 0 to 18446744073709551615
• LWORD: 64-bit unsigned integers, range 0 to 18446744073709551615
• REAL: 32-bit floating values, range -3.40282347E+38 to 3.40282347E+38
• LREAL: 64-bit floating values, range -1.7976931348623157E+308 to 1.7976931348623157E+308
• TIME: 32-bit words, range 0 to 1193h2m47s294ms
• DATE: 32-bit words, range 1970-01-01 to 2038-01-18
• STRING: Up to 252 characters, can contain ASCII codes from 0 to 255
Regards,
__________________
Garry
Old March 28th, 2017, 07:13 AM   #5
jrsnydley
United States
I believe that the 16 bit integer is the same as a signed integer isn't it? The only other option I have for a 16 bit is an unsigned integer. As I said, the data entry appears to give me what I want due to the scaling but the indicator tag for the numeric entry isn't showing any decimal places.
Old March 28th, 2017, 08:21 AM   #6
mike_dr
Yemen
mike_dr is offline
try increasing 5 field widthto 6. or try a new numeric display tag like gcl said. try moving to dint?
Old March 28th, 2017, 08:40 AM   #7
jrsnydley
United States
I have a 14 different numeric entries all tied to N7:110 to N7:123 through tags in the project in CCW. These were all pre-exisiting in a PanelBuilder 32 application. If I configure these as DINT tags won't that screw things up? I guess what I'm really wondering is if they can be configured as a Signed Integer in PanelBuilder, why does it act differently in CCW when I configure everything to be the same as it was?
Old March 28th, 2017, 09:23 AM   #8
jrsnydley
United States
Let me try to explain myself a little better. The operator, for example, will put in a value of 3.750 into the numeric entry. With the scaling, this shows up as 3750 in the MicroLogix. However, on the display for the current value of the tag, it shows a 4 because it won't display any decimal places and rounds the 3.750 up to 4. Is there a way I can get it to display the decimals so that the operator's input matches what is displayed on the screen?
Old October 30th, 2018, 05:34 AM   #9
pbaker88
Australia
pbaker88 is offline
pbaker88's Avatar
Hi Jrsnydley
Did you ever solve your issue??
I'm having a similar one with getting a decimal point to show with an INT on CCW with micrologix 1400.
Old October 30th, 2018, 06:59 AM   #10
jrsnydley
United States
This was a while ago so I am not 100% sure but I believe that I just changed it to a REAL and it worked correctly after that.
Reply
Bookmarks
Thread Tools
Display Modes
Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts
BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump
AB Micro800 and Connected Components Workbench programming question PLCDontUQuitOnMe LIVE PLC Questions And Answers 16 April 26th, 2017 07:02 PM
Connected Components Workbench Slow twocozz LIVE PLC Questions And Answers 3 December 1st, 2016 04:10 PM
Connected Components Workbench MarkNightingale LIVE PLC Questions And Answers 19 October 3rd, 2016 10:02 PM
Connected Components Workbench (CCW) and Allen Bradley Micro810 thesandbox LIVE PLC Questions And Answers 0 May 6th, 2012 01:47 PM
Connected Components Workbench Project ceilingwalker LIVE PLC Questions And Answers 0 April 4th, 2012 05:18 PM