1734 Modules Failing - Destroyed

Hello. I've been working through a problem at one of my customer sites where a section of 1734 I/O is getting destroyed. Excuse the long explanation, but the situation takes a bit of description. We have five production lines that are built heavily on the 1734 I/O via DeviceNet. The lines are about 10 years old, and in general we get great performance from the Point I/O along with the expected occasional module failure. In the last month we've had two lines create multiple failures in exactly the same way on their respective identical I/O racks. Each rack contains 20 I/O cards - mostly a mix of IB4, OB4, ITI, OE2V, IE2V, etc. Because of the I/O count we have a 1734-EP24DC. And 6 modules from the that we have a 1734-FPD that allows me to have some 5 volt stuff. All of the modules that fail are failing between these two power distributors. We get one random module that fails and is destroyed (Module Status goes red). Then at some point we'll get another module that fails, and these keeps going. In every case the modules are electrically destroyed. I spent several days carefully analyzing the first line, looking for thermal issues, contamination, errant electrical surges, etc. I inspected the failed modules under a microscope to see if there was any sign of obvious electrical damage - none. I discovered an issue with one of the wiring bases not reliably sending one of the network signals down the bus. At the end of the day I replaced the EP24DC, the FPD, all of the terminal bases, and all of the I/O modules. That line has been okay for a month now. We've started seeing this identical sequence of failure on another line. I would really like to understand how a sequence of destructive failure like this can occur. If anyone has ideas or similar experiences I'd love to hear about them - Thanks much!!
  Reply With Quote
Old June 15th, 2018, 03:31 PM   #2
harryting
Lifetime Supporting Member
United States

harryting is offline
 
harryting's Avatar
 
Join Date: May 2002
Location: Puget Sound
Posts: 1,825
Never had this happen to me, however, I do not use PointIO for mission critical stuff ever since I had two new AI module malfunction straight out the box.
  Reply With Quote
Old June 15th, 2018, 03:51 PM   #3
Ken Roach
Lifetime Supporting Member + Moderator
United States

Ken Roach is offline
 
Ken Roach's Avatar
 
Join Date: Apr 2002
Location: Seattle, WA
Posts: 14,110
I can't diagnose your system, but I'll tell you that overvoltage on the logic bus supply has caused similar results in 1734-ADN and 1734-PDN based systems I've troubleshot in the past.

On those systems they had some power supplies that failed and put over 50 volts onto the input of the 1734-PDN. While I/O is very well isolated from the logic bus, I think the bulk power supply is only limited and tested up to about 30 V. An intermittent short to 120V will definitely do the job too.

The report that one of the terminal bases wasn't reliably connecting the logic bus suggests that the modules are getting intermittent logic power; I've killed a 1734-AENT (a more complex module, sure) with a loose wire that caused rapid intermittent power disconnection.
  Reply With Quote
Old June 15th, 2018, 09:52 PM   #4
seth350
Member
United States

seth350 is offline
 
seth350's Avatar
 
Join Date: Jul 2011
Location: Over yonder
Posts: 233
We have the same issues except using 1734-AENT. Our rack consists of analog in/out, thermocouple modules and 120V outputs. We have had bases electrically burned, modules burned, modules that just quit working ( namely thermocouples), and bus controllers that just quit communicating.

When I first started digging into the issue, I found the bus was under supplied. There is a program from Rockwell that allows you to build a Point IO rack. The software will then recommend if you need to add EPACs or EP24DC modules in the rack and where. The rack we had was short two EP24DC modules. I installed them according to the software recommendations but we still have issues.

One thing I have learned is that the module bases are highly susceptible to moisture, dirt, and corrosion. The pins are not soldered to the board, they are just spring pins.
They do not like heat either.
__________________
“Did the Lord say that machines outta take the place of livin’, and what’s the substitute for bread and beans? Do engines get rewarded for their steam?” -John Henry
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
Using Point I/O with a CompactLogix 5370 controller technolog LIVE PLC Questions And Answers 14 October 28th, 2015 09:42 AM
selecting Modules for 1734 Point I/O danielswiatek LIVE PLC Questions And Answers 0 May 19th, 2015 08:22 AM
Point IO rack size the_msp LIVE PLC Questions And Answers 8 December 11th, 2014 11:26 AM
1734 Aent and Security modules Tarlo LIVE PLC Questions And Answers 5 December 30th, 2011 11:37 AM
Need help with config of 1734 IO over CNet wildswing LIVE PLC Questions And Answers 6 November 14th, 2011 01:42 PM


All times are GMT -5. The time now is 02:23 PM.


.