plc storereviewsdownloads
PLC training tools sale
Reply
Thread Tools Display Modes
Old September 25th, 2017, 09:11 PM   #1
freshmeat
China
freshmeat is offline
1734-ACNR PointIO
Hi Experts,
I got a 1734-ACNR failed on-site recently. I have replaced it with a new ACNR (node number and chassis size configured) but can't fix the problem.
As the system has been running for over an year (no update recently), it should not relating to programming/configuration issue I guess.
The ACNR modules status LED keeps flashing green and PointBus LED keeps flashing red simultaneously. Both channel A & B, System Power and Field Power LED are solid green.
The ACNR carrying totally 19 modules (IB8 and OB8 only) with 1 EP24DC in the middle. All IO modules modules status LED are solid green but network status LED keep flashing green. For the EP24DC, all LED on it are solid green.
There are other ACNR connecting to the same frontal and those are working just fine. The frontal is a ControlLogix L61 (16.54) with redundancy.
The ACNR replaced from site was tested on test platform and working so I am guessing something to do with TB, IO modules or EP24DC.
Any suggestion is appreciated.
Freshmeat
Old September 26th, 2017, 04:34 AM   #2
Maxkling
United States
Maxkling is offline
What is the fault showing in Logix?
What is the network status showing on the modules?
Old September 26th, 2017, 05:15 AM   #3
rdrast
United States
rdrast is offline
rdrast's Avatar
Firmware the same?
What do you see when you browse the network with RSNetworx?
__________________
How to ask questions the SMART Way!
Look First, Ask Second!
Old September 27th, 2017, 10:48 PM   #4
freshmeat
China
Thanks to your reply, I have checked the status on site.
The Fault code shown on Logix is 16#0010, Mode or state of modules does not allow object to perform requested service.
The Network Status on all IO modules are Flashing green.
Quote:
Originally Posted by rdrast View Post
Firmware the same?
The Firmware of ACNR is 1.83, same as other RIO.
On RSNetworx I can see the ACNR with 19 empty slots (chassis size configured to 20)
Also, when I checked the port diagnostic of the ACNR with RSLinx, the "Transmitted Good", "Received Good" and "Total Received" counters were increasing. The Network Update Time (NDT) is 5ms same as other RIO. I can only see the ACNR on RSLinx, no IO modules shown.
Hope this help.
Regards,
Freshmeat
Old September 28th, 2017, 03:15 AM   #5
rdrast
United States
rdrast is offline
rdrast's Avatar
No IO? Are you absolutely certain that the connecting fingers on the right side of the ACNR are actually mated with the first terminal base?
I've seen it where someone would change ONLY the ACNR, without removing terminal bases, and the adapter module didn't actually lock and connect to the terminal base next to it.
That many modules, you do have them broken up with some extra power supplies, right?
__________________
Old September 28th, 2017, 03:49 AM   #6
freshmeat
China
Hi rdrast,
Yes, I'm certain all terminal bases and ACNR are connected.
There is a EP24DC inserted between slot12 and slot13.
Feashmeat
Old September 28th, 2017, 04:50 AM   #7
MarkNightingale
United Kingdom
MarkNightingale is offline
I'm not sure about the ACNR, but for ethernet I/O you have to make sure the chassis size is set correctly.
Cheers
Mark
Old September 28th, 2017, 05:32 AM   #8
freshmeat
China
Hi MarkNightingale,
I have set the chassis size of ACNR and checked from RSLogix and RSLinx.
Freshmeat
Old September 28th, 2017, 05:55 AM   #9
MarkNightingale
United Kingdom
Sounds to me like you have a bent pin, or a missing pin on one of the connectors.
Old October 25th, 2017, 10:59 PM   #10
freshmeat
China
Hi Experts,
Sorry for late update.
The problem is resolved after replacing all 19 IO modules.
I have tested the IO modules replaced from site and none of them working, but the modules status LEDs are still showing solid green....
Thank you everyone.
Freshmeat
Reply
Bookmarks
Thread Tools
Display Modes
Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts
BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump
Issue Moving 1734 AENT From One PLC to Another Dave42 LIVE PLC Questions And Answers 10 September 7th, 2016 12:26 PM
PointIO 1734-OB8 and E-Stop jrsnydley LIVE PLC Questions And Answers 1 October 16th, 2015 02:42 PM
1734 ADN point i/0 adaptor jcperdue LIVE PLC Questions And Answers 2 March 4th, 2013 05:02 PM
1734 Aent and Security modules Tarlo LIVE PLC Questions And Answers 5 December 30th, 2011 12:37 PM
Need help with config of 1734 IO over CNet wildswing LIVE PLC Questions And Answers 6 November 14th, 2011 02:42 PM