1769-l32e Slow to achieve comms with Panelview 1000 plus

Hi All.
Im currently working on a project which entails copying a project from Plc and Hmi to a like for like system. I have managed to put the original programs on both, using Logix 5000 and Rs Factorytalk view studio. I have setup communication path in Hmi . The Hmi all operates ok but takes about 6 mins to initially achieve communication and load flags from plc. I think the issue may be Plc end as when i put newly programmed hmi in original machine it operates fine.

All Comms are done on Ethernet direct no switch. Any idea where i could be going wrong.
TIA
BLY
  Reply With Quote
Old October 29th, 2017, 12:29 PM   #2
widelto
Member
Colombia

widelto is offline
 
widelto's Avatar
 
Join Date: Jul 2005
Location: barranquilla
Posts: 2,580
Have you checked that your PLC or PV are not half duplex.
__________________
My two cents.
  Reply With Quote
Old October 30th, 2017, 12:38 AM   #3
Ken Roach
Lifetime Supporting Member + Moderator
United States

Ken Roach is online now
 
Ken Roach's Avatar
 
Join Date: Apr 2002
Location: Seattle, WA
Posts: 14,161
Welcome to the PLCTalk forum community !


>All Comms are done on Ethernet direct no switch.

Why ? Virtually all control systems that use Ethernet also need a port to allow access via an engineering workstation or enterprise network router.

Check the cable very carefully, and check the network status and link LEDs on both the controller and the PanelView Plus.

Another diagnostic method would be to make the first screen on the PV+ a FactoryTalk Diagnostic object, and see what the error messages are.

One of the things the modern PV+ does that the older ones didn't is that it checks every Tag in the HMI project to be sure it's available from the controller at startup. If you don't have a good connection (and yours sounds like there's a badly damaged port or cable), the PV+ can sit for quite a while trying to read all the tags, before it actually gets around to putting the HMI into operation.

Last edited by Ken Roach; October 30th, 2017 at 01:12 AM.
  Reply With Quote
Old October 30th, 2017, 03:17 AM   #4
Bly52
Member
United Kingdom

Bly52 is offline
 
Join Date: Oct 2017
Location: Northants
Posts: 2
Problem solved

Thanks for the response.
as it turns out there was a damaged cable between Plc and Hmi.

I have no idea why no switch installed as the system was inherited but maybe once all is running i will look at adding a switch.

Thank you for the assistance.
Bly52
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
clear application from Panelview 1000 sparksy@gage LIVE PLC Questions And Answers 3 October 16th, 2016 11:24 PM
comms problems between panelview and slc 5/04 LowRange LIVE PLC Questions And Answers 3 June 7th, 2016 10:36 PM
Connectivity between MicroLogix 1000 and PanelView C600 SergioB LIVE PLC Questions And Answers 20 January 5th, 2012 10:21 AM
Panelview 1000. messages showshocka LIVE PLC Questions And Answers 23 August 23rd, 2011 07:46 PM
Display String file on PanelView 1000 wa5yom LIVE PLC Questions And Answers 33 September 15th, 2003 10:53 AM


All times are GMT -5. The time now is 10:53 PM.


.