Old November 5th, 2017, 09:44 PM   #1
JZerb
Member
United States

JZerb is offline
 
Join Date: Oct 2016
Location: Highland
Posts: 90
ZipLink Module Serial Communication

So Im wondering if something is possible with these Zip Link feed through communication modules. If I have one in the control panel, and one out in a remote panel where the HMI is and Iím using it so that the two can communicate, can I plug into the unused port on the Zip Link and connect to the PLC from the remote panel location whilst the HMI is still plugged into the Zip Link as well? Or in order for me to be able to communicate with the PLC from the remote location will I have to unplug the HMI from the Zip Link and then plug my laptop into that port?
  Reply With Quote
Old November 6th, 2017, 07:46 AM   #2
gclshortt
Member
Canada

gclshortt is offline
 
gclshortt's Avatar
 
Join Date: Dec 2014
Location: Cobourg
Posts: 2,375
https://www.automationdirect.com/adc...Complete_List)

What PLC are you using? What communication port and protocol?

Regards,
__________________
Garry
http://www.accautomation.ca
Connect with us on Facebook: facebook.com/accautomation/
  Reply With Quote
Old November 6th, 2017, 12:45 PM   #3
JZerb
Member
United States

JZerb is offline
 
Join Date: Oct 2016
Location: Highland
Posts: 90
Micrologix 1200. RS232 DF-1. Using the programmer port on the side of it.
  Reply With Quote
Old November 6th, 2017, 12:55 PM   #4
OkiePC
Lifetime Supporting Member
United States

OkiePC is offline
 
OkiePC's Avatar
 
Join Date: Mar 2005
Location: ENE of Nowhere Oklahoma
Posts: 9,635
RS-232/DF1 is point to point meaning it only supports two devices. What you are wanting to do is supported by a port splitter from A/B part number 1747-DPS1. I have never used it, but I expect that your cable length will be limited to the RS-232 standard of 50 feet between the controllers.

What ZipLink module did you have in mind?
__________________
It's not all the variables I am most concerned with, it's the undiscovered constants.
  Reply With Quote
Old November 6th, 2017, 01:13 PM   #5
JZerb
Member
United States

JZerb is offline
 
Join Date: Oct 2016
Location: Highland
Posts: 90
This is the ZipLink I’m using.

https://www.automationdirect.com/adc...t)/ZL-RTB-DB09
  Reply With Quote
Old November 6th, 2017, 02:18 PM   #6
OkiePC
Lifetime Supporting Member
United States

OkiePC is offline
 
OkiePC's Avatar
 
Join Date: Mar 2005
Location: ENE of Nowhere Oklahoma
Posts: 9,635
I don't think that will work for you with three nodes connected at once. Using it as a terminal block interface between the PLCs should be fine and make for a professional termination. I think you will find that you need to unplug one PLC in order to connect your laptop to the other. The A/B port splitter has active electronics to enable it to "cheat" the electrical and protocol limitations.

In order to truly network the Micrologix 1200, if you have the budget, look at the Digi One IAP. It is a DF1 compatible serial to ethernet converter. This would allow the use of your PC and other devices like HMIs to all be connected to both PLCs. You would need two of them and they run about $400 each.
__________________
It's not all the variables I am most concerned with, it's the undiscovered constants.
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
MicroLogix 1400 RTD Module Jason Ozolins LIVE PLC Questions And Answers 8 June 14th, 2016 02:12 PM
Generic Ethernet Module communication status Lovell LIVE PLC Questions And Answers 4 May 13th, 2016 12:43 PM
serial communication between Siemens PLC and Arduino milan12 LIVE PLC Questions And Answers 13 September 11th, 2015 10:54 AM
URGENT: MicroLogix 1200 Serial Communication on Serial jawad rasool LIVE PLC Questions And Answers 11 May 24th, 2015 10:54 PM
slc 500 Problems with serial communication dms1808 LIVE PLC Questions And Answers 6 February 18th, 2009 06:38 AM


All times are GMT -5. The time now is 10:47 PM.


.