Old November 6th, 2017, 09:01 AM   #1
frodo88
Member
United States

frodo88 is offline
 
Join Date: Nov 2017
Location: Illinois
Posts: 2
Panleview Plus 600 won't grab the tags!

Hi,

I am fairly new to programming PLCs and HMIs. I have been tasked with converting a Panelview Standard application (Panel Builder 32) to Panelview plus 600. I was able to convert via FT studio and I was able to establish comms with my PLC (SLC 5/04) through DF1. If I go to RS Linx Enterprise in FT view I am able to add the DF1 driver and then browse to the PLC it is going to communicate with. I hit verify and I get these message for my shortcut saying;
"Path to design device is assigned [SLC Device]"
"Path to runtime device is assigned [SLC Device]"
and above these two notes I believe it displays the server name which is pretty long address. So here is my problem. Every time I run the application through the test run, I get these errors saying;
"Problem writing value to OT_CURRENT_SCREEN" (this is my welcome screen)
and it list bunch of addresses, for example
"Failed to resolve item's ID ::[slc]N7:002 because it does not exist on any server".
Can anyone point me in the right direction and tell me what I am missing? As I suspect, it is looking for tags but can't communicate or not sure where it is located at? Any help will be really appreciated.
  Reply With Quote
Old November 6th, 2017, 09:36 AM   #2
cwal61
Member
United States

cwal61 is offline
 
Join Date: Jan 2011
Location: NC
Posts: 884
The OT_CURRENT_SCREEN should be setup in the Global Connections under the display tab. You will find it under the System Folder in the explorer pane. There are two tag connections there one for Replace Display Number and another for Remote Display Number. If you are using the PLC to control opening the display each display must have a unique identifier. That tag must be returned to zero to allow operator control of displays.

The other addresses you need to make sure your shortcut names in the tags match the shortcut name in the communication setup. Also your tags need to be in the controller scope and not program scope tag database in the PLC. If you use program scope tags they must be identified in the tag connection.
  Reply With Quote
Old November 6th, 2017, 09:42 AM   #3
frodo88
Member
United States

frodo88 is offline
 
Join Date: Nov 2017
Location: Illinois
Posts: 2
Thank you Cwal61. I had my shortcut named differently then the actual address. It seems to be working fine now!
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
FactoryTalk View Studio Animation/Fill/Read from tags Reandy LIVE PLC Questions And Answers 9 June 22nd, 2017 11:03 AM
help with setup logix5000 tags lunknowl LIVE PLC Questions And Answers 6 June 1st, 2017 09:51 AM
Contrologix 5000: Program Tags vs Controller Tags Mark Snodgrass LIVE PLC Questions And Answers 5 June 10th, 2013 12:25 PM
Support for Panel View 600 Plus (Tags) McBacon LIVE PLC Questions And Answers 11 May 16th, 2013 11:01 AM
Generate HMI / SCADA tags from S7 project! nebula_1979 LIVE PLC Questions And Answers 1 November 18th, 2009 08:32 AM


All times are GMT -5. The time now is 06:35 PM.


.