plc storereviewsdownloads
PLC training tools sale
Reply
Thread Tools Display Modes
Old November 14th, 2017, 09:32 AM   #1
JohnCalderwood
Scotland
JohnCalderwood is offline
1756-L55 Clearing Memory
Some information for the folks on here.
We had a 1756-L55 clear its memory whilst running. The guys managed to power it down and reload an old backup to get it going.
The PLC was checked out by Rockwell - here is their response :
Quote:
The 1756-L55 debug.out diagnostic file has been analyzed, here is the report:
The Logix controller in your system experienced a Major Non-Recoverable Fault (MNRF). This specific MNRF was caused by a soft memory error. After careful review of the data provided to Rockwell Automation, it has been determined that this occurrence of a soft memory error was not caused by a firmware or hardware anomaly. The controller is working as expected. Furthermore, we have not seen soft memory errors caused by power, grounding, or electrical noise.
Logix controllers run a continuous series of background diagnostic tests including monitoring for soft memory errors. Diagnostic tests are performed to ensure the safe operation of the controller. If a soft memory error is encountered, a Major Non-Recoverable Fault (MNRF) will be declared by the controller. A MNRF is a controlled action taken by the controller when it is determined that the controller could no longer continue safe operation. When a Logix controller determines that a MNRF is the right course of action, the controller is designed to fault, taking it out of run mode, logging diagnostic data, and then invalidating and deleting the controllerís memory. This action requires an application program reload to guarantee the controller has a valid program to continue safe operation.
Never seen this one before, but we have a few ageing L55 PLCs, already changed one previously due to memory leak from InTouch 2014R2.
One to watch with the older processors I think....
Old November 14th, 2017, 12:17 PM   #2
harryting
United States
harryting is offline
harryting's Avatar
Well, that response said nothing that I can comprehend. Basically I took that as "**** happens".
We had a similar fault on a electronic trip relay (basically a controller) last year. It came back from the manufacturer as a "one-time abnormality"
I guess the good thing in all that the controller took itself out of commission before any bad stuff happens.
Old November 14th, 2017, 06:34 PM   #3
daba
United Kingdom
daba is offline
daba's Avatar
That's a very typical response you will get from RA.
Something went wrong....
The diagnostics did not tell us what....
The diagnostics did not tell us why, or where....
But the controller is working normally... That's what it does when it detects an error we can't tell you about, because we don't know, but rest assured, it is perfectly healthy !!
__________________
___________________________
ControlLogix & SLC Training
a-b train ltd.
abtrain@tiscali.co.uk
www.abtrain.co.uk
tel: 07506 73 9999
nil illegitimi carborundem
Old November 15th, 2017, 02:22 AM   #4
JohnCalderwood
Scotland
Aye, well....we could not take the chance.....the fault happened at a weekend.
We ran with the dodgy processor for less than a week, took the chance at the next shut and replaced the processor...
Old November 15th, 2017, 06:03 AM   #5
rdrast
United States
rdrast is offline
rdrast's Avatar
Maybe a high energy cosmic ray just happened to zap a particular bit in memory.
I've had that happen though as well, but I don't bother wasting time with Rockwell on it. Typically, I've always seen it with a power off, or sag, with the battery backup not holding. Especially on L55's, the backup there was measured in minutes if lucky, unless the external BATM module was used.
__________________
How to ask questions the SMART Way!
Look First, Ask Second!
Old November 15th, 2017, 09:10 AM   #6
lanester
United Kingdom
lanester is offline
I've also had this in the past with a L55 on one machine on multiple occasions. It could run months without issue. Firmware & battery change made no difference. Replaced the processor in the end and the issue went away.
Old November 19th, 2017, 07:37 AM   #7
BinderNut
United States
BinderNut is offline
We had two machines with L55s that would randomly do the same. New processors, replaced batteries, firmware updates, etc...always the same thing.
We finally upgraded the processors to L61s for firmware support reasons (when we upgraded our PCs to Win7 64-bit) and we haven't had the problem since.
Reply
Bookmarks
Thread Tools
Display Modes
Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts
BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump
Read S7-200 Memory Cartridge zgendron LIVE PLC Questions And Answers 0 September 25th, 2015 02:08 PM
Micrologix 1100 memory module kolyur LIVE PLC Questions And Answers 5 June 24th, 2015 09:50 AM
TwidoSuite Memory junior LIVE PLC Questions And Answers 2 January 25th, 2011 12:21 PM
S7-200 download project from memory carrtridge ason LIVE PLC Questions And Answers 5 October 16th, 2006 04:25 PM
SLC 5/03 data loss andydaoust LIVE PLC Questions And Answers 1 October 10th, 2002 06:38 PM