3 phase motor partial winding start

I have a customer with an old pump panel which uses autotransformer style reduced voltage starter. I have worked with wye/delta starters, but this is my first experience with this variation of reduced voltage starter. The old panel is a rusty mess so the plan is to replace it with a VFD to allow ramping up to speed and limiting the upper end. This is driving a 125 HP water pump supplying a distribution system (including water towers).

The word is that when they last ran the pump (more than a year ago) it blew up water lines so now they will not run it. There are two other pumps teed into their system that are 75HP and one of them has a soft starter. Right now, they only run the smaller pump on the soft starter.

I would expect that this is probably as simple as connecting the motor as shown in the "RUN CONN" diagram, carefully setting up the VFD parameters and starting it up with caution like any other pump. I do want to proceed with caution and would like to hear any input from the motor/drive experts.

Thanks!
Paul
Attached Images
File Type: jpg part start 125hp B.jpg (62.2 KB, 73 views)
__________________
It's not all the variables I am most concerned with, it's the undiscovered constants.
  Reply With Quote
Old November 22nd, 2017, 04:35 PM   #2
jraef
Member
United States

jraef is offline
 
jraef's Avatar
 
Join Date: May 2006
Location: Northern California
Posts: 1,550
Yes, you would connect it in the Run pattern permanently. just make sure to buy a VFD rated for 142A minimum, which shouldn't be an issue for anything calling itself 125HP. If the pump is centrifugal, you can use a "Normal Duty" / "Variable Torque" rated drive, but if you aren't sure, just get a Heavy Duty / Constant Torque version, it's the safe bet.

My one cautionary statement is that this is an old motor, designed before VFDs existed and without protection, it will not likely last long. To get the most life out of it, add at least a DV/DT filter to the output side of the VFD, a Sine Wave filter is better (but more $$). Or, you can do what a lot of people do; run it to destruction as is and then replace it with an Inverter Duty motor. But consider your down time costs with that route.
  Reply With Quote
Old November 22nd, 2017, 09:15 PM   #3
OkiePC
Lifetime Supporting Member
United States

OkiePC is offline
 
OkiePC's Avatar
 
Join Date: Mar 2005
Location: ENE of Nowhere Oklahoma
Posts: 9,854
Quote:
Originally Posted by jraef View Post
Yes, you would connect it in the Run pattern permanently. just make sure to buy a VFD rated for 142A minimum, which shouldn't be an issue for anything calling itself 125HP. If the pump is centrifugal, you can use a "Normal Duty" / "Variable Torque" rated drive, but if you aren't sure, just get a Heavy Duty / Constant Torque version, it's the safe bet.

My one cautionary statement is that this is an old motor, designed before VFDs existed and without protection, it will not likely last long. To get the most life out of it, add at least a DV/DT filter to the output side of the VFD, a Sine Wave filter is better (but more $$). Or, you can do what a lot of people do; run it to destruction as is and then replace it with an Inverter Duty motor. But consider your down time costs with that route.
Thanks!

I had planned on advising the customer and providing options for a filter and disclaiming our company from insulation breakdown if they choose to run without a filter. We will do megger tests at the outset in any case.
__________________
It's not all the variables I am most concerned with, it's the undiscovered constants.
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
Mechanical/Material Handling and ISA 88 rlmunoz LIVE PLC Questions And Answers 7 October 11th, 2018 08:45 AM
using AB Powerflex as a third phase for 3 phase 230V motor ! leonlai LIVE PLC Questions And Answers 16 February 9th, 2016 03:10 PM
programming exercises drummin89 LIVE PLC Questions And Answers 5 September 10th, 2012 05:45 AM
What do you call this voltage joeparrish LIVE PLC Questions And Answers 52 October 15th, 2008 02:20 AM
Automation or not ? Pierre LIVE PLC Questions And Answers 23 May 26th, 2004 06:06 AM


All times are GMT -5. The time now is 03:51 AM.


.