plc storereviewsdownloads
PLC training tools sale
Reply
Thread Tools Display Modes
Old November 24th, 2017, 04:45 AM   #1
DLMUK
United Kingdom
DLMUK is offline
ATEX Intrisic Safety (IS) question.
I have an application which is in an ATEX hazardous area, the instrument being used is lower power and qualifies as 'simple apparatus' and is connected from the safe area via an IS barrier.
The setup is:
Instrument -> cable -> barrier -> safe zone
What I would like to know is, if we put a connector on the cable half way down its length, but within the hazardous area, does it require and ATEX approval?
As the power is limited by the barrier before the connector, I can see an argument that the connector type doesn't matter. I have also seen applications where both ATEX and non ATEX connectors are used.
thanks
Old November 24th, 2017, 05:30 AM   #2
Rob...
Supporting Member
United Kingdom
Rob... is offline
What type of connector? Just terminals?
Are you altering the characteristics of the loop? E.g adding any capacitance/impedance?
I'd be wary with calling items 'simple apparatus' unless certified as such by the manufacturer. To certify yourself you need to prove it meets around 7 BS EN Standards. Some of which needs lab testing to verify.
Old November 24th, 2017, 05:36 AM   #3
DLMUK
United Kingdom
DLMUK is offline
@Rob
thanks for the reply. The item has already been confirmed as Simple Apparatus by an authorized UK test house.
What we want to do is just add a connector to help with installation and maintenance. So that the instrument can be easily removed for calibration. It would therefore be an inline cable end connector, one male and female receptacle.
We haven't specified a connector as unsure what is required at present. Something along these lines would be good:
https://uk.rs-online.com/web/p/mil-s...ctors/2982409/
thanks
Old November 24th, 2017, 05:50 AM   #4
Rob...
Supporting Member
United Kingdom
Rob... is offline
I would think that as it has been passed through a barrier you're ok using something like that. I'll have to check though.
Regulations will most likely stipulate that it can't be plugged or unplugged whilst the circuit is energized.
Old November 24th, 2017, 08:22 AM   #5
cardosocea
United Kingdom
cardosocea is offline
You will still require that the plug conforms to the IP rating for that particular area (or perhaps it's fixed for IP65).
And the distances to the 3mm to earth and 6 between different loops.
Most likely and to err on the side of caution, anything Exe will do. I would also try to find a connector with an end cap to protect the terminals if the sensor is to be removed and not replaced. I don't think it is required, but can protect you concerning the condition of the loop.
I would also have a quick look on the rating for dust as the conditions compared to gas and vapours are different.
Old November 25th, 2017, 05:54 AM   #6
Friedrich
Sweden
Friedrich is offline
As stated by Rob there shouldn't be a problem as long as you don't add impedance or capacitance to the circuit, which you don't if the connector is just that. The connector doesn't need to be Atex approved since it's part of the IS loop. Just make sure you document it in you IS system description for that circuit.
Old November 25th, 2017, 09:04 PM   #7
James Mcquade
United States
James Mcquade is offline
DLMUK,
if by connector, you are referring to terminal block, it depends on the environment.
if by connector you mean a micro connector, it still depends on the environment.
what ever the environment, you must use a seal off within 18" of the safe zone. the seal off being in the hazardous area. Rigid pipe, myers hubs, and conductive sealant ( not sure on this in the UK) as well.
the terminal block or connector must also meet certain criteria. I do not know the current UK rules, so please check.
cheers,
james
Reply
Bookmarks
Thread Tools
Display Modes
Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts
BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump
Safety Lock Status in Safety Program Kalagaraz LIVE PLC Questions And Answers 0 May 11th, 2017 10:15 AM
Trying to understand safety PLC's (specifically Siemens) Jieve LIVE PLC Questions And Answers 3 June 24th, 2014 09:27 AM
Safety PLC for dummies Wilso LIVE PLC Questions And Answers 10 October 18th, 2013 08:48 PM
Question about Safety Switches wdd0422 LIVE PLC Questions And Answers 4 January 7th, 2013 10:57 PM
Safety PLCs? Karsten LIVE PLC Questions And Answers 38 January 4th, 2012 03:30 PM