plc storereviewsdownloads
PLC training tools sale
Reply
Thread Tools Display Modes
Old November 28th, 2017, 04:52 PM   #1
d.dinh
Australia
d.dinh is offline
RSLogix 5000 PIDE Cascade
Hi all,
Having some issues setting up a PIDE Cascade control loop.
Have been trying to go through the Wp008 doc but there's probably something easy/small that I'm missing.
I have a tank with an oil jacket which is directly heated up using resistive heaters (SSR). The oil jacket in turn heat transfers to the tank product (wax).
The application is heat only, as the client generally turns on the oil jacket heaters and leaves overnight for the wax to melt.
Am I correct in assuming that this calls for a PIDE Cascade Loop?
Primary Loop - Wax Temperature - 4-20mA - 0-200C with SP cutoff at 150.
Secondary Loop - Oil Jacket Temperature - as above.
Secondary Loop output goes to SRTP for the SSR output.
Thanks ahead for any help.
d.dinh
Old November 29th, 2017, 12:23 PM   #2
rankhornjp
United States
rankhornjp is offline
right click on all your "wires" that go from the PID on the right to the PID on the left, and click "Assume data available"
Old November 30th, 2017, 05:40 PM   #3
d.dinh
Australia
d.dinh is offline
Quote:
Thanks mate. Did work it out in the end. But was a quite frustrating process trying to figure what I had done wrong.
Does anyone know whether "assuming data available" is in the white papers/manuals anywhere?
Old November 30th, 2017, 05:50 PM   #4
raffles
Canada
raffles is offline
It's in the FB programming manual, page 14
http://literature.rockwellautomation...m009_-en-p.pdf
Old December 1st, 2017, 03:30 AM   #5
rdrast
United States
rdrast is offline
rdrast's Avatar
I'm not seeing where you need cascaded loops here...Honestly, I'm not seeing where you even need two, perhaps a diagram?
__________________
How to ask questions the SMART Way!
Look First, Ask Second!
Old December 3rd, 2017, 05:14 PM   #6
d.dinh
Australia
d.dinh is offline
Quote:
Here's a quick sketch.
I am not exactly sure whether the client/operators control the wax temperature as the setpoint, or the oil jacket temperature as the setpoint.
But essentially, they heat up the oil using a pair resistive heaters that are turned on using solid state relays(on/off only).
As the oil heats up, the wax product heats up.
They generally leave this on overnight at the set temp so the wax melts overnight without supervision (apart from PLC).
Old December 4th, 2017, 04:42 AM   #7
rdrast
United States
rdrast is offline
rdrast's Avatar
I really don't see any need for cascaded loops there.
Run one PID for the oil temp, and one for the wax temp. Done.
__________________
Old December 4th, 2017, 06:18 AM   #8
jamesau
United States
jamesau is offline
Quote:
I'd try to find out more from them about their process/product.
I'd like to think the melting wax behaves as any other melting-solid process. Specifically, the solid temperature rises until it reaches a solid/liquid transition temperature (or temperature range). The temperature of the melting product remains relatively constant until all is melted and then the all-liquid product temperature begins to rise. As an analogy, think of heating a block of ice; the ice block temperature will rise until it reaches 0C/32F and stay at that temperature until it is completely melted. The water temperature will then rise towards the temperature of its surroundings.
For a process as described above, I would simply control oil temperature at some high level, wait for the wax temperature to indicate all has melted, and then set the oil temperature to some melt-maintenance temperature. (And note different temperature schedules/recipes might be necessary for different wax products).
Old December 4th, 2017, 07:01 AM   #9
d.dinh
Australia
d.dinh is offline
Sorry. You have me a little confused (and probably my limited understanding).
If I were to use two separate PIDs, would the output of the Wax temp PID control? I only have the one SSR to control the heaters that heats up the oil only.
Old December 4th, 2017, 09:58 PM   #10
d.dinh
Australia
d.dinh is offline
Quote:
I will have to double check at the client's old site and with the previous OEM they used for the PID loop controllers.
But how it was explained to from an operator's PoV:
When they start the heating process:
- the heaters will turn on and get the oil jacket temp up to 145C
- the wax product temp SP will be something like 120/130
- as the wax temp PV gets towards the SP, the heaters back off so the oil temp PV also backs off to keep the Wax temp at its SP.
- main reason for the over temp of the oil vs the wax is so the wax melts faster to reduce waiting time
- heaters turn on/off as required to maintain wax temp PV at the SP.
Hopefully that makes sense. Anyone have further thoughts on this?
Cascade PIDE control or not? Similar applications done in the past?
Many thanks,
d.dinh
Reply
Bookmarks
Thread Tools
Display Modes
Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts
BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump
How to access other ASIC registers in Rslogix 5000? csjokerd1123 LIVE PLC Questions And Answers 0 August 18th, 2017 01:48 AM
RSLogix v20 - PIDE Cascade setup. KristienP LIVE PLC Questions And Answers 2 January 27th, 2016 11:55 AM
RSLogix 5000 Read Only Access? chrisj91 LIVE PLC Questions And Answers 5 September 19th, 2014 11:23 AM
Pid Cascade Loops Rslogix 5000 learner LIVE PLC Questions And Answers 5 November 23rd, 2008 06:36 PM
RSLogix 5000 V15 Features Samneggs LIVE PLC Questions And Answers 18 April 20th, 2006 05:45 PM