Star Delta Starter with Timer Relay or with PLC Timer
Star Delta Starter with Timer Relay or with PLC Timer.
Any preferences?
Any reasons one way or another?
Old November 29th, 2017, 07:07 AM   #2
gclshortt
Canada
gclshortt is offline
gclshortt's Avatar
It is really up to you and the functionality of the system.
Regards,
__________________
Garry
https://www.accautomation.ca
Connect with us on Facebook: facebook.com/accautomation/
Old November 29th, 2017, 07:31 AM   #3
slp530
United Kingdom
slp530 is offline
A mechanical star delta time has a small time delay between the Star-delta changeover also use mechanically interlocked contractors for Star delta
Old November 29th, 2017, 07:56 AM   #4
renan.musardo
Brazil
renan.musardo is offline
Quote:
Any preferences?
If I already had a PLC, I'd use the PLC timer instead of a timer relay.
But it really depends on you. The final result will be the same.
Old November 29th, 2017, 11:31 AM   #5
moggie
England
moggie is offline
moggie's Avatar
Any preferences?
Timer relay - anyone can change the time delay without the need for software or interface cables.
Old November 29th, 2017, 11:50 AM   #6
jraef
United States
jraef is offline
jraef's Avatar
Quote:
The transition time is more of an art than science, because the load on the motor makes a difference. You want that to be easy.
And as said earlier, there are really TWO time delays involved in a Star-Delta transition timer. Electro-mechanical timers do it via contact operating times, electronic S-D timers have to emulate that, which is not a simple thing in a PLC. Not impossible, but you have to fully and deeply understand the process. Not enough or too much of an open transition time can cause severe damage, both electrically and physically. I've seen open transition problems cause a 500HP motor shaft to shear off.
That's also why I never use S-D any more, I use RVSS starters.
Old November 29th, 2017, 11:55 AM   #7
Ronnie Sullivan
United Kingdom
Ronnie Sullivan is offline
Plc timer every time
Use mechanical interlocks and inputs from the n/c of star and delta.
It's not often a timer needs adjusting once set correctly.
Old November 29th, 2017, 01:22 PM   #8
Gene Bond
United States
Gene Bond is offline
Quote:
If I had to use one, I'd go with a separate timer, so *when* the PLC has to be bypassed for whatever reason (with an HOA switch or whatever), I could still safely start the motor...
Old January 7th, 2018, 03:34 PM   #9
AustralIan
United Kingdom
Thanks all, I think I like the idea of a PLC timer with mechanically interlocked contacts best, but in the end it is probably not priority 1 at the moment to evangelise either way.
Agree with RVSS for higher kW applications.
My new years resolution is to phase out imperial measurements, especially the mile, which I will be replacing with 1.852km, unless the person specifically tells me they are working with the international mile.
I am also going to assume metric horsepower, ie. the power to raise 75kg by 1m in 1 second under 9.80665 N/kg of gravity.
Old January 8th, 2018, 06:25 AM   #10
saultgeorge
United States
saultgeorge is offline
I would agree with jraef for sure regarding RV starters over S - D. I worked for a large water utility for 10 years out west, and we had mostly 5kv motors with RVAT starters. The transition, incomplete sequence, etc. used relays. A-B made a good one. We re-wired a lot of them to transition on current using a GE Multilin 469 MPR. It has a lot of capabilities that certainly surpass relay logic, but it is quite expensive.
__________________
Detroit City Limit: An Automation Alley Community
Old January 8th, 2018, 10:40 PM   #11
Bering C Sparky
United States
Bering C Sparky is offline
Bering C Sparky's Avatar
What is this wicked metric heresy speak.....LOL
__________________
Changes in Latitude = Changes in Attitude
*********Florida - Seattle - Alaska****************
"I WANT MY LOGIX BACK"
Reply
Bookmarks
Thread Tools
Display Modes
Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts
BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump
PLC Delta communication problem, Any help ? wadi2000 LIVE PLC Questions And Answers 1 November 24th, 2018 08:27 AM
Delta plc real time clock splendid8877 LIVE PLC Questions And Answers 4 September 30th, 2016 09:25 PM
CLICK PLC Short Timer (5ms) Nubbb LIVE PLC Questions And Answers 11 February 3rd, 2014 10:52 AM
How to communicate to Delta PLC from PC ( connected via RS232) MANISH VORA LIVE PLC Questions And Answers 8 September 25th, 2012 09:08 AM
Connection of delta VFD with plc m_faraz LIVE PLC Questions And Answers 1 February 22nd, 2011 07:51 AM