plc storereviewsdownloads
PLC training tools sale
Reply
Thread Tools Display Modes
Old December 2nd, 2017, 05:22 AM   #1
panthripu
India
panthripu is offline
water flow control valve
Hello everyone
I need some suggestion from you. We are controlling the flow of water in one of application. Our problem is the set point is fluctuating and due to this the valve is continued hunting and hence the flow is also fluctuating. Our requirement is not very critical that the flow should be exactly same as setpoint +/- 5 to 10% error is acceptable. Any ideas , how to tackle it.
Note: We tried filter in PLC for the input signal, tried to adjust damping the valve. But the results are not desirable.
Old December 2nd, 2017, 09:59 AM   #2
cjd1965
United Kingdom
cjd1965 is offline
the setpoint is fluctuating? You mean the flow is changing and your valve is not responding to adjust within a suitable time?
Sound like your PID settings need tuned better
Does the control valve have a positioner (intelligent controller) or just 4-20mA /3-15 psi ?
Old December 2nd, 2017, 11:40 AM   #3
Bit_Bucket_07
United States
Bit_Bucket_07 is offline
Bit_Bucket_07's Avatar
Quote:
Originally Posted by panthripu View Post
Hello everyone
I am going to assume that your SP actually is fluctuating, which would indicate a cascade loop in which a different loop controller is establishing the water flow loop's setpoint.
I have encountered a similar situation in which a water flow loop's setpoint was mathematically derived to maintain a specific ratio with the amount of dry material that was being added to a mixer by a weigh-feeder belt conveyor. I was able to achieve more stability in the water flow loop by deriving the water flow loop setpoint via the weigh-feeder's SP, rather than from the weigh-feeder's CV. I also implemented SP deviation alarms that would halt the process in the event that either the water flow or the solids delivery went too far out of spec.
I don't know if any of that helps in your situation, but if your SP is very unstable, I would think that you'd get better results by finding a way to stabilize the SP changes somewhat.
__________________
Old December 2nd, 2017, 12:05 PM   #4
daba
United Kingdom
daba is offline
daba's Avatar
I don't know what the problem is - if the flow loop SP is changing, then it is right and proper that the valve should be fluctuating, and hence the water flow.
You could slow-down the valve fluctuations by giving the PID less Integral gain, and remove any Derivative, but it will still try to follow the SP, only slower.
You could "fix" your flow control valve at a steady position for a number of seconds at a time.
You will need to accumulate total flows over time, and step-change your fcv setpoint up or down according to the error.
__________________
___________________________
ControlLogix & SLC Training
a-b train ltd.
abtrain@tiscali.co.uk
www.abtrain.co.uk
tel: 07506 73 9999
nil illegitimi carborundem
Old December 3rd, 2017, 05:47 PM   #5
Tom Jenkins
United States
Tom Jenkins is offline
Tom Jenkins's Avatar
If the problem is that the valve hunts after a change in position command you could try to open up the deadband on the positioner.
Old December 3rd, 2017, 06:02 PM   #6
Mickey
United States
Mickey is offline
Mickey's Avatar
Why ?? Please explain.
__________________
Mickey
If you want happiness for an hour-take a nap. If you want happiness for a day-go fishing. If you want happiness for a month-getmarried. If you want happiness for a year-inherit a fortune. If you want happiness for a lifetime-help someone else.
----- Chinese Proverb
Old December 4th, 2017, 11:11 AM   #7
panthripu
India
control valve
Set point is variable, its process requirement.
If a fixed set point is used, the valve responds very nicely. But in normal operation , when the valve tries to reach to the set point , by this time new set point is recieved. And this change in set point is within 2 to 3 seconds.
Old December 4th, 2017, 11:55 AM   #8
Mickey
United States
Mickey is offline
Mickey's Avatar
If these changes in set-point are not to big and given the tolerances you posted above, I would consider filtering the set-point changes as others have suggested.
File Type: txt Filtering.txt (292 Bytes, 16 views)
__________________
Mickey
Old December 4th, 2017, 04:15 PM   #9
shooter
Netherlands
shooter is offline
shooter's Avatar
please slow down the setpoint by using a ramp on the setpoint.
__________________
shooter@home.nl
skype shooter paul.deelen
Computer Shooter
Paul Deelen
J. Wassenaerstraat 29
NL 5224 GG 's-Hertogenbosch
+31653300739
Old December 5th, 2017, 03:50 PM   #10
hoy7t
United States
hoy7t is offline
How fast do update the PID loop?
There is the delay between sending a setpoint and seeing the first indication of a change in the feedback. This is called dead time.
You can measure deadtime. Let the loop stabilize. Then make a change to the control output. Then measure elapsed time until you see an observable change in the process variable (PV).
Fr'instance:
If the pump takes 1 second to change flow such that it can be detected by your PID loop (PV), then your PID loop cannot respond any faster than one second. After any update, your logic must wait at least the deadtime, preferably longer, before making another update.
If the PID loop updates faster than deadtime then it is responding more than one time to the original PV. This might cause the control output (CO) to oscillate or hunt.
If integral gain is applied, then the output is phase shifted, and it will be more likely to oscillate.
Reply
Bookmarks
Thread Tools
Display Modes
Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts
BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump
PID Help travispedley LIVE PLC Questions And Answers 11 June 27th, 2017 09:54 AM
Temp and Flow Control for two pumps aemcgo0 LIVE PLC Questions And Answers 11 March 27th, 2015 08:53 AM
PID valve control valahia@gmail.com LIVE PLC Questions And Answers 2 April 15th, 2012 01:45 PM
3 way Control Valve from Siemens with Beckhoff PLC tech007 LIVE PLC Questions And Answers 0 April 6th, 2011 05:00 AM
Boiler Fuel Feed Simulation for Bunker C sjknight LIVE PLC Questions And Answers 1 November 20th, 2005 04:42 PM