plc storereviewsdownloads
PLC training tools sale
Reply
Thread Tools Display Modes
Old December 4th, 2017, 11:04 AM   #1
PerryMB
United States
PerryMB is offline
1769-AENTR Fault Control
I have 1769-L35E CompactLogix controller communicating to two 1769-AENTR. While testing, I can pull the Ethernet cable and I get a major fault. Does anyone know of way to turn this feature off so I can use logic to determine if I have a communication problem?
Thanks,
Old December 4th, 2017, 11:16 AM   #2
Ken Roach
United States
Ken Roach is offline
Ken Roach's Avatar
Welcome to the PLCTalk Forum community !
Look at the Connection tab for the 1769-AENTR in the Studio 5000 I/O tree. There is a checkbox for "Major Fault on Controller if Connection Fails in Run Mode".
It's probably checked in your system, so un-check it. You can do so online in Run mode.
Have a look through the Forum or the RA Knowledgebase on how to use GSV instructions to detect I/O connection status.
Old December 4th, 2017, 11:16 AM   #3
MarkNightingale
United Kingdom
MarkNightingale is offline
You need to go to the properties of the module.
Then on the connection tab, untick the box that says major fault on controller.
Cheers
Mark
Old December 4th, 2017, 11:17 AM   #4
Robobob
United States
Robobob is offline
Robobob's Avatar
Double click on the 1769-AENTR in the I/O tree. On the connection tab you can select if you want to Major fault the CPU or not.
Old December 4th, 2017, 12:13 PM   #5
PerryMB
United States
PerryMB is offline
Thanks for all the replies.
I do have the check boxes unchecked.
Old December 4th, 2017, 02:00 PM   #6
Ken Roach
United States
Ken Roach's Avatar
I don't have direct experience with the 1769-AENTR but I believe that it bridges a module connection to each of the 31 possible connected modules, rather than using a "rack optimized" connection like the 1734-AENT or 1756-ENBT can.
So check the Connection tab for each of the connected 1769 modules connected to each Adapter.
If all that doesn't work, trigger the fault and review the fault code and we'll see if it points us toward a different root cause.
Old December 5th, 2017, 06:48 AM   #7
PerryMB
United States
PerryMB is offline
Ken,
I checked connection tab on each input and output card and they had the Major Fault check. I assume that connection tab on the 1769-AENTR would determine if a fault would happen. You know what they say about assuming.
Thanks for the tip.
Old January 18th, 2018, 03:14 PM   #8
ronny_resistor
Canada
ronny_resistor is offline
ronny_resistor's Avatar
GSV and AENTR
OK this may or may not be a good place for this question. I have approximately 10 AENTR units and each has a web page that one could look at. I noticed that there are error counters and other really cool information. This is not about that.
So when we start loosing information we would like to see the error counters or information that tells me that the Ethernet connection is about to be dropped out.
With Remote I/O we had a bunch of counters that could be monitored and based on the retry numbers we could say "Clean your wire path"
So with a GSV instruction we can see if a module has failed or if the status of the lights but what about retry counters or missed communication or packet errors, is there a way to read these from my modules ???
Forgot to mention there are sliprings involved and I need a way that lets me know that oxidation is starting to effect my data. Hence "Clean your wire path"
Reply
Bookmarks
Thread Tools
Display Modes
Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts
BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump
Need advice regarding reset/clear fault (Motor Fault) backendcode LIVE PLC Questions And Answers 3 September 18th, 2017 12:22 PM
Fault In Proximity Sensor! backendcode LIVE PLC Questions And Answers 15 September 12th, 2017 06:00 AM
How to reset G120 fault over ProfiNet? AdamG8GXP LIVE PLC Questions And Answers 33 September 29th, 2014 11:41 PM
control logix 5000 major fault problem Britt LIVE PLC Questions And Answers 0 March 29th, 2011 02:55 AM
AB 1336 - fault, parameter defaults and "out of range" mxx LIVE PLC Questions And Answers 2 November 25th, 2010 09:19 AM