Old December 5th, 2017, 09:29 AM   #1
technolog
Lifetime Supporting Member
United States

technolog is offline
 
Join Date: May 2015
Location: Ohio
Posts: 125
SLC 5/03 indirect addressing error

I'm trying to set up a 1746-HSCE2 high speed counter module in a SLC500 with a SLC 5/03 processor. The manual - http://literature.rockwellautomation...m002_-en-p.pdf - gives an application example on page 6-7 using indirect addressing. However, when I try to verify the project, I get an error saying "Indirect addressing is not supported on the current processor type for the N file type".

The manual states that indirect addressing will only work with SLC 5/03 and higher processors. I have an SLC 5/03. The example in the manual also uses the N file type, so I don't know what the problem is.

The offending instruction is

COP

Source #N12:[N13:0]
Dest #O:5.0
Length 8

If anyone could offer any insight, it would be very much appreciated.
  Reply With Quote
Old December 5th, 2017, 12:08 PM   #2
Mickey
Lifetime Supporting Member
United States

Mickey is offline
 
Mickey's Avatar
 
Join Date: May 2003
Location: Palmdale,Ca
Posts: 10,075
Quote:
Using Indirect Word Addresses
You have the option of using indirect word-level and bit-level addresses for
instructions specifying word addresses when using an SLC 5/03 (OS302), SLC
5/04 (OS401), or SLC 5/05 processors.
The operating sytem needs to be OS302 or higher, yours is?
__________________
Mickey

If you want happiness for an hour-take a nap. If you want happiness for a day-go fishing. If you want happiness for a month-getmarried. If you want happiness for a year-inherit a fortune. If you want happiness for a lifetime-help someone else.
----- Chinese Proverb
  Reply With Quote
Old December 5th, 2017, 12:16 PM   #3
technolog
Lifetime Supporting Member
United States

technolog is offline
 
Join Date: May 2015
Location: Ohio
Posts: 125
OS301 :-)

I went ahead and did the programming using direct addressing and have both encoders counting, I'm very pleased to report. Out of interest though, is it possible to change the OS and if so, how?
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
Indirect Addressing Error After Converting from PLC-5 to ControlLogix kevc2181 LIVE PLC Questions And Answers 6 August 25th, 2016 07:52 PM
HMI - Issues setting up indirect addressing BennieC LIVE PLC Questions And Answers 11 August 20th, 2016 04:58 PM
Error Handling in SLC 5/03 husnain.mahmood LIVE PLC Questions And Answers 11 October 12th, 2009 12:10 PM
PLC5 and Indirect Addressing kdcui LIVE PLC Questions And Answers 3 October 23rd, 2008 09:46 AM
SLC Indirect Addressing gluca LIVE PLC Questions And Answers 7 July 23rd, 2002 06:49 PM


All times are GMT -5. The time now is 12:13 PM.


.